I am working with a PLC5/40C and am having some problems with the configuariton of one of the PID loops.
The max output paramater was originally set at 100% but has changed to 81%. I attempted to reset the value to 100, but when I weent back in the new avaluew was not displayed. Is there a lock that could be in effect? Also, can you make changes to PID on-Line?
Jack
Check to see if something in the program or HMI/SCADA is writing to that parameter.
Post your .RSP file ( zip it first ) and someone can help you look. Tell us which PID if you have more then one.
Jack
Welcome to the Forum!
There is no lock for the PLC5 PID that I am aware of. Yes, you can make changes to the PID Online, but be very careful. Putting an invalid Value in can Fault the PLC.
Is it possible the Value is being overwritten in the PLC Program somewhere or by an HMI?
For more information on the PLC5 PID Instruction, have a look at Chapter 14 of this Manual.
http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1785-rm001_-en-p.pdf
Stu....
Good Call. This PID controls an inlet pressure to an environmental system. If th outlet pressure gets too high, it clamps the inlet hi limit.
Thanks for the advice.
jack
Has anyone had an issue with a PID control after the processor has been upgraded form a L40E to a L80E. It does not seem to be controlling...
48
6,048
I am working on a PLC5 that is doing temp control. However the temp control is working more like ON/OFF and not Proportional control. I am not...
32
8,782
Has anyone ever converted a the PID instruction from a PLC5 to a CLX platform? The issue I am facing concerns the difference between a PID...
3,492
I'm working on a project to convert an old PLC5 processor to an L63. Below is sample logic of one of the several PID controls from the...
5,050
Hey fellas, I'm in the midst of doing my first translation from 5 to 5000 that also includes PID instructions. I'm just looking for any helpful...
5,547