My customer has a powder tablet pressing machine from a company not longer in business. I was asked to replace the feedback from the load cell from the original controllers to an analog PLC card from AD 260CPU.
Question:
Based on the specs I have for this load cell, does anyone know what component I need between the Load Cell and the analog PLC?
Specs:
GAUGE EXCITATION VOLTAGE: 10.00 VDC
CHANNEL NUMBER: 2
PRESS MOUNTED GAUGE CALIBRATION: 2.8329 mV/V
@ CALIBRATED LOAD: 6.96 TONS
MAX. GAUGE OUTPUT:28.3 mVDC.
FIXED GAIN RESISTOR: 1.18K OHMS.
MAX.PRESS LOAD: 20.00
RATIO=1: 0.3478
Thanks for your help
How fast is the press running (PPM)? These presses can run very fast you need to make sure that any signal conditioner is quick enough for the speed of the press. You should also check the speed of the analog input. One last thing is to look at what is to be done with the analog input. If it is to be used for die protection you may need something faster than you will get with a PLC.
Can anyone recommend a supplier for these signal amplifiers-conditioners?
CharlesM:
The signal will be used for adjusting the stroke length, on the fly. A servo will be doing the adjusting in response to the strain gauge signal.
I am working on an experimental system for a new chemical a supplier of a client of mine has invented and my customer is going to be their Guinea...
21
5,794
Hi all, I was assigned to develop an architecture for the system in which i have to calculate the amount of powder that will be inleted in to a...
1,730
We have a photo sensor to monitor the flow of starch but coz of the dusty environment the sensor is generating teh fales alarm. Putting the...
37
7,717
Can any one tell me which is the best On Line measurement system for Milk Powder Moisture measurement. At the moment I have 2 in mind : 1) MM710...
3,518
Looking for some hands on user's experience setting steel bolts into steel using powder actuated gun. The PLAN 1. Set chiller into place and...
25
5,456