Power consumption
Charbel
Jan 2012
Beirut
307
Dear,
i was looking at the attached control devices from schneider and how to estimate the power consumption,
from the attached and clouded, i can depict that since the current per channel is 0.5A at 24V, i can say that the maximum power consumption is 0.5*16*24 = 192W.
Please advice.
Charbel
This seems to be the base only. Hence the idea of either inputs or outputs
The 2 amp protection fuse and the 1.8 amp limit for the common.
Dear iant,
thank you for your quick response, in this case, how do u think the power consumption can be computed?
Your calculations are based on absolute maximum power. This is normaly never achieved
You could have twenty 10 amp power points in a house but you don't use 200 amps do you.
You need to look at what will be running at any one time.
There has been many posts about interposing relays
This is how you protect your PLC outputs.
As far as 24 Vdc power supplies I find most small machines need no more than 2.5 amps total
I have seen and wired machines with 20 or 30 amp supplies. But these are very large machines
For DC power supplies I use the new ones from Omron - they are not much more than the Taiwanese ones and are much better quality. I quite often use 8-10 amp DC power supplies as I have to feed power to many external devices including remote touch screens and the like. 10 amps for under $80au - cheap as and good quality too.
In regards to similar kind of topic I wanted to ask a simple question.
I have an Ultrasonic Level Transmitter operated on 24 V DC with an output of 20mA and maximum error Amps as 22 mA.
So does it mean that the maximum power consumption of this Transmitter is 24*22=0.528 Watt ??
(converting mA to Amperes)
Please correct me
P=V*I
V=I*R
Rt= sum or all R's in the cct
Correct yourself if you need to
I was wondering if anyone had any insight on to how i could monitor and possibly graph Amp draw on our Powerflex 525 Drives. These drives are...
1,774
Hello, I want to ask about the power consumption of the 1769-Pb4: It is written that the input power consumption at maximum load is equal to...
1,832
Hi All, I'm having some trouble on determining the total power consumption of the following I/O modules: 1769-OB32,1769-OF8V, 1769- OW16...
2,650
Hello We have a 3 phase machine where we need to log the power use during every run of a process. Each run can last anywhere from 30min to 5...
2,296
Dear, I am computing a rough estimate on the power consumption for UPS for a PLC cabinet, the UPS will be also serving two flowmeters (each...
1,579