Power status with contact make break in odinary electrical relays
royanabil
Sep 2011
Kolkata
I hv designed an UPS power distribution system where the computers hosting the application are connected to two single mode UPS through an ordinary electrical relay. The configuration is that the primary UPS excites the relay coil and a NO contact of the relay makes to loop power to the computers. The line and phase from the secondary UPS is connecetd to a NC contact of the same relay such that in event of primary UPS failure, the NC contact loops power to the computers with no interruption in power supplied to the computers.
Will this configuration work fine or there will be a reboot for the computers during the relay contacts switch over?
Honestly, if uptime is that important, I'd keep the two UPS units, but invest in a computer with dual redundant power supplies.
Would your idea work? Possibly, but it depends entirely on the connected computer. Most current high efficiency computer power supplies don't have a very long hold time, usually only a few cycles of the incoming power.
the data centres use seperate supplies.
Two large UPS which then keep a battery bank fully charged.
two battery bank converts the DC bus to a 'Clean' AC supplies.
not to mention automatic bypass back to mains.
Most Servers, at that level, use dual supplies.
This is not a new design
How important is this project for you to redesign the wheel?
Hello Members We have a controllogix redundancy setup and need to display the status of redundancy in panelview. I have found in the manual the...
1,264
I am new to Mitsubishi GX2 and GX3 software here at work. It is common practice to use an "M" memory bit as a temporary bypass. This is done by...
718
I’m using RSLinx to get some of the built in diagnostics items from the PLC. Like @ProcessorName, gets you the name of the program running in...
1,277
Dear all, I would like to hear Some suggestions for Capturing Power fail status and Power resumed status in Micro logic 1400 My requirement is...
1,584
Fellow PLC Lovers :nodi:, Good day! I'm back again for another question. This time for Modicon M340. I am currently developing a user program...
3,113