Power Supply Heat Loss
Engineer_UA
Oct 2016
California
43
Greetings,
When the cut sheet for a power supply states that the heat losses are 20 Watt for a 240 Watt DC-DC converter, does this mean that the power supply consumes 260 Watt at full load? Since the data sheet assures the specifier that the PS will deliver 10Amps at 24Vdc, it would make sense that the heat losses are on top of 240W rated value.
Thanks,
Engineer_UA
It sounds like a reasonable assumption. The rated value would need to reflect the output capability in order to be valid, and energy lost is energy lost.
I have the power supply in the link below. If we want a breaker to isolate and protect the input side how would I size that correctly being 120...
204
I am looking for power supply that I can mount on vertical DIN rail, and when mount that way is =< 4" wide. this is what I have now.... this is...
21
583
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
439
We've still got a ton a PLC 5's installed and running. We lost a 1771-P7 Series B power supply. There are a lot of 1771-P7 series D power...
239
Long ago, it was often a customer spec to always use a transformer for isolation of the control circuit from the rest of the equipment. For 24vdc...
681