I'm trying to setup a PowerFlex 4. Having problem with the Acc/Decel time. Parameter P039 (Acc), P040 (Decel) will not responsed to any time setting that is enter into these parameter.
Also there is a DB resistor accross the braking terminals. I'm I missing a setting that must be entered?
thanks
rmonroe
That settign means DC injection braking which is the reason the decel time has no effect.
The DB resistor will help the drive dissipate regeneration caused by overhauling loads or rapid deceleration.
DC injection braking can stop a motor pretty fast, sometimes faster than the minimum ramp time. It depends on the inertia of the rotor and the load. It also may cause some motor heating depending on how much current is being injected for what duration, and how often it executes this braking cycle.
If you want a longer decel time, try changing P37 to 0 or 4 (0=Ramp to Stop and Clear Faults, 4=Ramp Stop).
Thanks for your help.
I set the parameter 37 to setting 4 and now we have braking...
rmonroe
Looking for some assistance. I am very familiar with Yaskawa VFDs, but not so much with AB VFDs. I am working on some hardwired AB PowerFlex 700...
149
Hello, I am playing around with a Powerflex 525, I am able to run the drive via RSlogix 5000 over ethernet. I am curious on how to set drive...
650
Hello Everyone, I have multiple machines that do the same thing, only the IP's are different. Some of the machines have AB drives while others...
16
1,251
Howdy, very happy to have found this forum. I purchased a piece of equipment (canning line) that has an old PF 40 drive. It ran fine for a...
1,193
I have a client that wants software backups of all drive parameters, so I am going to connect via CCW. Obviously, they would prefer to not stop...
1,960