PowerFlex 70 & 700 Fault Resets
curlyandshemp
Jul 2005
Toronto
1,903
I am on a startup that has several VFDs and E3 overloads on Device Net. This morning when I walked in, 5 of 8 of the VFDs, PowerFlex 70s and PowerFlex 700s, were all displaying OverVoltage Faults. Apparently a powersurge occured through the area overnight. What I don't get is why the PowerFlex's did not fault reset. I always have logic, that worked in the past, to reset a fault automatically.
Code attached along with UDT assigned to bits for the PowerFlex command work via the Comm-20 D.
I had to manually reset all the faults using the HIM module attached to each drive
PowerFlex 700 Fault Clr
Good morning:
Just a check of a few things you might look at.
Param 241 (Fault Clear Mode) should be set to Enabled.
Confirm Communication file param 271, bit 3 is set to true.
Check Diagnostics Param 226 to confirm what the DC bus voltage was at the time of the fault.
(Param 174 default = false: and ONLY enabled if you desire to attempt an autostart after the fault is cleared.)
Your PP1_VFD.CLEAR_FAULT ONS Param 240 to true?
I hope this helps.
Curly, is this a conditional routine or does it run continuously?
If it runs every scan, then you will constantly be trying to clear faults as they occur. What if the drive can't clear the fault? The PLC logic will not stop trying...
Might be useful to have an operator/tech push a button to trigger the fault clear logic. I usually tie drive reset logic to a master reset button somehwere...
Maybe the drive reset logic went true during the power spike, the drive could not clear the fault, then power went off and came back on with the fault logic true the whole while.
What happens if the drive powers up and the fault_clear bit is already true? The drive might need to see a false to true transition of the fault_clear bit.
Another thing you might do is add an internal bit address (that you can toggle from RSLogix)in parallel with theexisting code to reset the drive fault via devicenet rather than use the HIM module. That would at least let you test the devicenet reset logic.
Just my observations. Let us know what you find.
Paul
Not sure if the Powerflex is the same as the older A-B Plus II drives but I think they are, it will basically act like a one shot rising instruction. So if the fault was not clear yet, and you trigger a fault reset, it might not reset. Holding the fault reset will not keep triggering resets. Just once.
So if this is the only way you have to reset the drive, you might want to look at cycling the reset on and off periodically. That's if you want to make certain the drive will reset automatically from the program.
Hi , I have an Allen Bradley Powerflex 700 Inverter It has a green power light ( led ) and under that has a status Light ( led ) The...
2,255
Hi all, i have a powerflex 700 Alen Bradley drive. I recently got a fault on the drive. I am not familiar with these units and wanted to ask...
2,087
Running a Powerflex 700 VC 40, two 10 hp motors in parallel with their own overcurrent protection, FVC mode, Intertia autotune done, external...
7,052
I've set up a powerflex 700 with Digital Input 1 (set to Stop - CF), and wired a pushbutton to give the input to clear faults. I've verified that...
3,618
I have a Powerflex 753 that shows a fault code "212 safety jumper out" upon powerup of the vfd. The jumper is in place and there is the same fault...
5,183