I have a powerflex 70 connected to a compactlogix L32E via a N-Tron 708tx switch. My problem is my L32E has stopped communicating with my drive.
A while back we had a short and it smoked my ethernet switch, I replaced the switch, but since then i lost comms to my drive. I thought since I got stray voltage thru the switch maybe it smoked the ethernet adapter, I have replaced the 20-COMM-E ethernet adapter, the patch cable, as well as the drive itself. Still nothing.My panelview plus 1250 communicates just fine (also on the ethernet). I get on to the controller and i can see it trying to connect to the drive, but then it says cannot connect. Any Ideas on what might have happened? I know my IP address is right, and all the parameters on the flex 70 are correct. I am at a loss.
First, verify IP connectivity to the PowerFlex from that switch.
Start with good old PING, then try TCPing [Link] on TCP Port 44818.
The embedded Web page isn't enabled by default, but you can try using a Web browser to see if something appears at the 20-COMM-E's IP address.
Next see if the PowerFlex appears in an RSLinx Classic browse. If the PowerFlex appears there, you can start troubleshooting the configuration and connection to the 1769-L32E controller itself.
See if you can capture the connection error code in RSLogix 5000. For example, Error 0x0204 is a complete timeout, while Error 0x0203 indicates a rejected connection for some other reason.
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
321
Hi guys! We have a big project at work where we are migrating from 1305, 1336, 160, 70, and 40 drives to identical PowerFlex 525 models. Most...
905
Hello, I have an existing application that has a Powerflex 700 with a 20-COMM-E adapter controlled by a Micrologix 1100 via Ethernet. The setup...
1,205
I have a contractor at my water plant installing 3 brand new Powerflex 7000 VFD's for my High Service pumps. I would like to control these via...
1,022
Hi All, I am working on testing a project with a Powerflex 525, final project will be a 755, and I am trying to reset the Elapsed kWh meter over...
612