Powerflex 753 drive overload fault

Elijah58

Member
Join Date
Nov 2012
Location
Aiken, SC
Posts
60
Guys,
I have a powerflex 753 25hp that we installed replacing a powerflex 700 25hp. we had a short that took out the drive and we installed a powerflex 700 20hp just to get by till we got the 753 in. the 20 hp seemed to work fine except when we got into a heavy load and then would fault at about 29 amps. when we installed the 753 everything seemed ok but started getting a "Motor Overload Fault" and shutting the machine down. Parameters in the 700 25hp and the 753 25hp. are the same but it is kicking out at around 23 amps. motor is 460 V rated at 25hp 26FLA. Has anyone run across this issue with this drive.
Thanks in Advance,
Eli
 
Are you running at a speed that results in an RPM below 20 Hz? The drive comes with a default configuration that assumes a TEFC motor construction. The drive applies a derating curve to the continuous current at at output frequencies below 20 Hz. This can be configured so it is effectively ignored.

Keith
 
The PF 750's are EXTREMELY sensitive to just about everything out of the box. Check P413, "Mtr OL Factor", it defaults to 100%, I bump it up to at least 125.
Actually, I have had to go so far as to set the Motor OL Actn (P410) to "Alarm".

While you are at it, take a look at P463 "InPhase Loss Lvl"... That I set at 1000, and also set the "InPhase LossActn" (P462) to "Alarm" as well.

Then there is also P409 "Dec Inhibit Actn" that I also set to either ignore or Alarm.
 
I have seen about a 10% failure of PowerFlex drives OUT OF THE BOX. I would start a tech support ticket which you will need to exchange it.
 
RDRAST Thank You, This has solved the problem, we have run production since yesterday without any issues whatsoever. I am so greatful to have a site like this to come to for help, It has helped me many times, just wish I was a little more knowledgeable to be able to give something back.

ianingram: the motor is a BLUE MAX, on a SEW gearbox.
Thanks Again,
Eli
 
Blue Max motors in that horsepower rating are TENV (totally enclosed non-ventilated) construction. They are physically designed to dissipate all the heat they generate down to zero speed without air-over cooling. So you are good.

Keith
 

Similar Topics

Hey all, I wanted to discuss an issue with achieving a constant flow rate of around 10 GPM on a glycol circulation pumps in a 1200-1300 PSI...
Replies
4
Views
987
Hi, I'm trying to add an AB Power Flex 753 drive to an old device-net network, we have 6 different drives (700's) and and 2 I/O adapters, now I...
Replies
3
Views
1,897
Dear All, I need urgent help for my powerflex drive 753 showing error port x06 not functioning (conflicts) i tried to find out soluction from...
Replies
4
Views
4,997
Good Afternoon , Powerflex 753 seems confusing just to configure a input. A coworker installed a pushbutton to use as a fault reset for a...
Replies
4
Views
4,037
Good Evening , I have a PowerFlex 753 that I need to replace . There will be a 20-750-S and a 20-750-ENETR installed . I uploaded a...
Replies
3
Views
2,771
Back
Top Bottom