Hi
I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or does it wipe everything and starts again with the firmware.
And I have to reload the program ?
Thanks stu
 
Firmware updates will wipe your program. You should sign up for a Rockwell account if you don't already have one. You are looking for the "Product Compatibility and Download center". Get Connected Components Workbench if you don't already have it. You also might want to get ControlFlash Plus. It's really nice and will look online and download firmware kits for you.

Ethernet is generally the easiest way. Even if you need to get a dumb switch and connect right at the drive. The HIM has a copycat function - be aware that you need to use this for all peripherals. The IO board, the EENet, Port 0 (the actual drive), and the onboard devicelogix.

CCW is totally the best way. Make sure you can find your drive in RSLinx. Then make a new CCW project, add a device, in the top right, add an existing device. Then navigate to it in RSLinx. Then, upload the parameters from it. Save your project. Then, fire up controlflash plus and use RSLinx to navigate to your drive. Get the desired firmware revision, and you can go ahead and flash the drive.

Back in CCW, update your module definition to your new firmware, then do a download.

That should be it.

NOTE: If this drive is being controlled by a PLC, you will almost certainly have to perform a download if you upgrade firmware, so a lot of times its easier to just use controlflash or controlflash plus to flash the firmware DOWN to the current revision in the controller. Just turn off bootp, set the drive's IP, subnet mask and possibly gateway, reboot the drive, inhibit the drive in your PLC, then you can flash the drive and put the parameters on it.

EDIT: If you reset parameters via the HIM or CCW, your IP address will be lost and you have to go put it back in. If you flash the firmware with controlflash, the IP address will remain.
 

Similar Topics

So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
278
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
142
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
Replies
3
Views
228
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
Replies
10
Views
434
Need some help trying to set the IP address in a Powerflex 755 with a 20-HIM-A3 installed. Drive has an embedded Ethernet card from the factory...
Replies
4
Views
265
Back
Top Bottom