Hi guys,

I am new in siemens software and trying to go online with a plc S7 300 via router, this is what i have been doing, first i connect my vmware station to a wireless router, assign automatic IP address, the PLC is connected to the same router via cable.

when i set the pc/pg interfase it shows a good connection, but when I loof for available nodes, nothing appears, even i can ping the PLC and the aswer is pretty good.

I am using the Step7 professional V5.5 sp2, any help would be really appreciated!!!!

best regards
 
have you selected right ethernet interface from: set PG/PC interface on step7?

Try first connecting plc with ethernet cable directly to PC, can you see plc then?
 
I understand your Step7 is under VMware right?
Try change network from NAT to bridged and test again.

Also try to get connected straight to plc first, although going through router does not not make any difference as long as you are on same IP class.
 

Similar Topics

Hi, Im pretty much inexperienced with Control logix platform. We have a new machine that has controls done with it. Problem is I cannot...
Replies
0
Views
1,625
Its great to be able to contribute something for once after having used the forum. ANyhow, a particular 2 * 7 rack SLC system has been a...
Replies
1
Views
2,310
I have arranged a spare PLC5 for our machine which already has PLC5. After receiving, I set the dip switch settings same like the original...
Replies
11
Views
5,074
I am trying to go online with a Micro with Proficy ME software. I have a cable IC200CBL500A. When I try to go online, I cannot connect. This PLC...
Replies
34
Views
11,412
Dear PLC Experts, I am trying to go online with Omron Sysmac CPM2A PLC with CX-Programmer V 6.0 on Windows Vista Operating System. It gives...
Replies
7
Views
9,771
Back
Top Bottom