Problem in Interfacing Quantum PLC with RSlogix5000 via EIP
kondababu
Jan 2016
Hyderabad
I'm working in Schneider PLC platform and not aware of RSlogix. In my new project I need to communicate my Quantum PLC with 1756-L55 controller with 1756-ENBT/A module over Ethernet/IP Protocol. I configured NOC78100 module as master in my PLC by adding 1756-ENBT/A EDS file. But I'm not able to establish the communication. NOC configuration is attached here
Please help me is there any configuration required to change in RSlogix side????
By adding the EDS file to the NOC's configuration you should be able to consume a tag using Rockwell's Produced/Consumed tag mechanism. You would have to configure the Logix platform, through RSLogix, to produce that tag.
Alternatively, you can reverse the communications and make the Logix the scanner (will require configuration) and the NOC the adapter (the NOC has several local adapters or slaves that can be configured). At least this way you will be able to send and receive data. With the consumed tag, the NOC can only receive data.
There are other threads on here referring to this type of communication - EtherNet/IP Class 1 between Schneider and Rockwell devices.
Hi everyone, I am facing a problem with my F5 series KEB Frequency drive. I have cobivis5 software and HSP5 service cable for interfacing. i am...
2,130
I'm trying to interface plc and scada where scada is monitoring and controlling the parameter using MODBUSA3 protocol but SCADA is not sending 05...
1,706
Hi, I am khairul beginner plc programmar. Now i face a problem that how i direct add an incremental rotary encoder to Mitsubishi FX2N/FX1N,S7-200...
2,033
Problem for interfacing SR2B121JD with my window7 32bit Pc.I am using Zeliosoft 2. when I go to communication configuration under transfer menu. A...
1,485
The project on the operator workstation keeps disconnecting, even though I have an installation server and operating station set up through...
51