hello,
I received a used Analog Output Module 6ES5 470-4UC12 (ES 902 design for S5-135/155)
I tried to mount it in the S5-115U PLC in Central Rack CR 700-3 in free slot number 2 (using 6ES5491-0LB11 ADAPTER CASING, F. S5-115 F. 2 MODULES).
I set module address 176 (with DIP switch), which address is not used by any other module.
Next I connected 24VDC Power supply in to the terminal 3 (L +) and 21 (L-).
I connected everything in accordance with the instructions (I use only 4...20 mA outputs) and began testing.
In Step5 I wrote the statement:
L KM 01000000 00000000
T PW 176
but the PLC is an error QVZ (no access to the I/O PY177).
I also tried the block FB251:
: JU FB 251
XE : FW 250 ;PHYSICAL OUTPUT VALUE
BG : KF +176 ;CARD ADDRESS: 176
KNKT: KY 0,0 ;CHANNEL:0; 0=UNI-/1=BI-POLAR
OGR : KF +3041 ;UPPER PHYS. LIMIT:
UGR : KF +0 ;LOWER PHYS. LIMIT:
FEH : F 0.2 ;ERROR BIT
BU : F 0.3
PLC not stopped, but then F0.2 (BIT ERROR) = 1
When I measured with ammeter, on all outputs 4... 20 mA there was 0 mA
Is the 470-4UC12 module corrupt ?????
Hi!
I have never tried what you are doing here, but I doubt that you can set the card adress with the switches on the card. You probably should set the 470 switches in a certain pattern, I guess all off. If you have got an IM306 in the rack, try to adress it there. Else I would suppose that it's automatically adressed according to place number.
Btw, did you apply the voltage to enable the output channels (if it is relevant for 470)?
Kalle
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
121
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
18
1,462
Hello All!! I am new to the forum and have seen alot of good answers so far, but I have not been able to resolve the issue I am having. :mddr...
4,301
Dear friends, Presently I am working in a water treatment plant where T&C is going on, we are using VFD to control motors while...
8,025
Good day guys (and gals) I have a question about what is required to get an analog output from a em232 analog output module connected to an s200...
6,089