profibus / modbus
Hello!
You can use the following Prosoft industrial gateway Profibus Slave to Modbus Master/Slave 5105-MCM-PDPS. Connect this module as Profibus Slave to S7-300 as Profibus Master. And then connect your VFDs as Modbus Slaves to Prosoft Gateway as Modbus Master.
http://www.prosoft-technology.com/P...bus-Master-Slave-to-PROFIBUS-DP-Slave-Gateway
http://www.prosoft-technology.com/content/download/1205/9015/version/5/file/MCM_PDPS_Datasheet.pdf
I use different Prosoft modules for a long time and they work pretty well. And Prosoft tech support is great also.
Hello!
thank you for your replay
Do you have any examples for using s7-300/400 using this gatway
No, unfortunately I have never used this gateway. But you won't meet any problem with it. You add GSD file of gateway in your Step7 project and connect it to your PLC as Profibus DP slave.
Then you need to configure the gateway with Prosoft Configuration Builder software to work as Modbus Master and connect your VFDs as Slaves. You can find more info in gateway's manual.
Regards, Oleksandr.
I've done some profiNET (not profiBUS) to modbus RTU using anybus module.
The main thing is to understand and strictly follow the modbus standard. For example, to set a single coil (1 bit) you don't write a 1...you write 0xFF00 (16 bits) but to write multiple coils you write bytes using 1 bit/coil. Also modbus RTU is even parity by default so best stick to that...if you need to run no parity, then you need to set up for two stop bits to maintain 10bits/byte....lots of little gotchas in the modbus standards. If it isn't working, dig into the modbus spec, and find what you are doing wrong...my experience is that it behaves very robustly once you get things correct.
Hi Everyone! I am feeling some troubles while dealing with Profibus and Modbus. Is there anyone who can help me out in following questions? 1...
2,505
hello I use S7-317 CPU in new project to control production line. I use two old DC motor drives...in old configuration they were controlled...
1,758
Hi, On a project, i have to assess the possibilities of communication directly from a Labview application on a computer. Profibus: you need a...
3,285
Hi all I want your advice for my problem : I have two PLC control systems , first is an old one and I use an Intouch Scada system to monitor and...
3,400
I have a Pfister Universal CSC Controller that has a CAN-Bus/Modbus-RTU port for networking but I have a profibus networking. Now I want to make...
1,622