Profibus/modbus
May 2007
giza
153
hello
I use S7-317 CPU in new project to control production line.
I use two old DC motor drives...in old configuration they were controlled using unitelway protocol.
NOW I will use modbus-rtu...... for limited budget I can not use CP341/340
I will use HILSCHER gateway nt 100-dp-rs.
I want to change parameters of ramp up/down "as attached it W22,23" and some other digital bits
Actually Iam very new with modbus communication. and also in using this gateway.
can any one help in how can I transfer date to W22,23 using this gateway from his experience or by example
https://www.hilscher.com/fileadmin/cms_upload/en-US/Resources/pdf/Configuration_of_Gateway_and_Proxy_Devices_OI_08_EN.pdf
The gateway manual will show you where to put the address for the modbus rtu locations.
What you are looking for is the modbus addresses of the drive.
http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/31000/FA31595/es_ES/Rectivar%20User%20Manual.pdf
Here is the option board for the drive modbus information.
http://www.sarl-hallier.fr/Files/Other/SCHNEIDER/TRIES/VARIATEURS%20CC/RECTIVAR%204%20EXTENSION.pdf
Here is some additional information on Modbus RTU:
https://www.rtaautomation.com/technologies/modbus-rtu/
Hope this helps you out.
Regards,
Hi Everyone! I am feeling some troubles while dealing with Profibus and Modbus. Is there anyone who can help me out in following questions? 1...
2,509
Iam working on link PLC S7-317 2PN/DP as master using profibus to two old slave speed drives which have only modbus (rs-485) after search I...
2,021
Hi, On a project, i have to assess the possibilities of communication directly from a Labview application on a computer. Profibus: you need a...
3,289
Hi all I want your advice for my problem : I have two PLC control systems , first is an old one and I use an Intouch Scada system to monitor and...
3,402
I have a Pfister Universal CSC Controller that has a CAN-Bus/Modbus-RTU port for networking but I have a profibus networking. Now I want to make...
1,623