Hello,
I have been trying to set up a PB network between 3 s7-CPU315-2DP v2.6 , but i couldn't...
Here is the connection:
Slave1: A2----------A1 :Slave2: A2-----------A1 : Master
B2----------B1 B2-----------A2
Distances between nodes are quite long , about 600m. That's why i've chosen 187.5Kbps for baud rate.
I have combined all PLC's in the same Simatic Manager project and did the configuration necessary(at least i think so
Strange problem is; when i disconnect Slave1's PB cable, the CPU indicates a bus fault. When i connect it back, the bus fault is OK. But on the other nodes, there is a permanent bus fault(?).
And another strange point is, when i download HW to Slave1, CPU switches to RUN mode properly, however no output becomes active. I get online to check it out and i see that some outputs are seem to be set in software, but in fact no relay gets energised.
I would really be very happy if someone helped, because i am running out of time
Regards,
I have been trying to set up a PB network between 3 s7-CPU315-2DP v2.6 , but i couldn't...
Here is the connection:
Slave1: A2----------A1 :Slave2: A2-----------A1 : Master
B2----------B1 B2-----------A2
Distances between nodes are quite long , about 600m. That's why i've chosen 187.5Kbps for baud rate.
I have combined all PLC's in the same Simatic Manager project and did the configuration necessary(at least i think so
Strange problem is; when i disconnect Slave1's PB cable, the CPU indicates a bus fault. When i connect it back, the bus fault is OK. But on the other nodes, there is a permanent bus fault(?).
And another strange point is, when i download HW to Slave1, CPU switches to RUN mode properly, however no output becomes active. I get online to check it out and i see that some outputs are seem to be set in software, but in fact no relay gets energised.
I would really be very happy if someone helped, because i am running out of time
Regards,