Profibus[Omron inverter - Siemens Plc]
pokajy
Mar 2008
Turkish
53
Hi
I want to control omron f7 inverter with s7-300 plc with profibus.
If someone made similar project, can u share? or some documents.
I've profibus module for f7 inverters.
Thank you
Is the Omron really a Yaskawa?
If so- there is a sample in the "downloads" section of this forum.
If not- post the .gsd file and manual-
This will help us all to help you
Yeah it's yaskawa. I checked example. it says it's for yaskawa magnetek gpd315. i think it'll work for my f7 inverter too.
I'll test it soon.Thank you
there is no hardware in yaskawa magnetek gpd315 example project.
in omron webpage (library files by type/gsd file )
I just found this gsd.
GSD file for the 3G3AX-MX2-PRT ( PROFIBUS DP Slave interface for MX2 Inverter)
I looked through the gsd
This is an EASY one. This gsd uses PPO types and this is typical.
Pick my sample of PPO4 (telegram 352) in the "downloads" of this forum
Its called g120driv.zip
Just modify the names ie..control word..status word names to match the Omron
Then your set
Get it working??
Hi!
Can anyone help regarding the flexible i/o mapping type?
i just want to access the following parameters so that i can display it through the HMI via s7 300 plc... I am using a Mx2 omron drive link in a profibus network..
Power - kWh
current - Amperes
Total running hours
torque
thanks in advance!
Hi!! There is existing project Step 7 whith 20 frequency inverters Danfoss. Can I add to this project/real hardware 4 Omron frequency inverters? I...
5,103
What is the difference between ths CS1W-PRM21 and C200H-PRM21? I am trying to setup my hardware in the PLC program but only see the CS1W-PRM21...
2,049
Hi, When I search for answers I often come to this site. Although I don't always find what I need, there seems to be a lot of knowledgeable...
2,854
I have a cpu315-2 dp set up as the master and an Omron Prt21 card set up as a slave and i was wondering if there is a way to transmit a data block...
3,829
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
195