profibus problem
gh_ounie
Dec 2007
aleppo
73
Dear all , good day
Our system is S7315-2DP, and the DP is define as DP Slave, connected to DCS system from another company we transfer the data between two (master and slave) through Profibus MS protocol (slot 4,5,6)
And the system is working fine without any problem for more than three years.
Now, we need to send more information from PLC to DCS, so we add a new MS slot (slot 7), , and then I download it to PLC
The PLC after that is still working in Run mode but the BF and SF LED are ON, and all the data communication between DCS and PLC was lost.
gh ounie.
1st, I think you should post the diagnostic buffer in this thread.
The PM you sent me contained 2 links, one to some kind of program that I dont want to open, and the other to a RAR file with probably the diagnostics buffer. Unfortunately I cannot open RAR files, so I think you should just post it as a ZIP file.
Now is this problem with the same PLC and DCS as the other thread ?
If so, then I am genuinly confused, because in that thread you talk about a Yokogawa DCS and an S7 PLC connected together as master-to-master via a DP coupler (each partner sees the other partner as a slave).
If this is another project, and it is really an S7 setup as a DP slave, then my best guess at the moment is that only one side is correctly setup.
The full diagnostics buffer will probably tell us more.
i'm so sorry to confused you and i'm realy appreciate your helping this is a new project and this is the
Diagnostic buffer of module CPU 315-2 DP -part 1
Order No./ Description Component Version
6ES7 315-2AG10-0AB0 Hardware 3
- - - Firmware V 2.0.8
rack: 0
Slot: 2
Event 1 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
03:45:55:271 am 09/30/97
Event 2 of 10: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
03:45:55:269 am 09/30/97
Event 3 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
Last valid operation or setting of the automatic startup type at power on:
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
03:45:54:591 am 09/30/97
Event 4 of 10: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
03:45:43:055 am 09/30/97
Event 5 of 10: Event ID 16# 4304
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Incoming event
03:45:15:396 am 09/30/97
So:
  • What is the problem?
  • There are any things to do or modify in our PLC or user program or any SFC or DB,…
I’m waiting your reply with best regards.
and this is a part 2
Event 6 of 10: Event ID 16# 4302
Incoming event
03:40:15:270 am 09/30/97
Event 7 of 10: Event ID 16# 1381
Priority class: 27
Incoming event
03:40:15:268 am 09/30/97
Event 8 of 10: Event ID 16# 4301
Incoming event
03:40:14:587 am 09/30/97
Event 9 of 10: Event ID 16# 5371
Incoming event
03:40:03:011 am 09/30/97
Event 10 of 10: Event ID 16# 4304
Incoming event
03:39:37:314 am 09/30/97
Incoming event
Priority class: 27
Incoming event
Incoming event
Incoming event
Incoming event
Is this the same as the other thread, or is it a different problem ?
Did you update the DCS partner in the same way as the S7 PLC ?
The diagnostics buffer does not say so much.
Only one I can see is the "difference between setpoint and actual configuration".
Maybe it means that the partner isnt configured in the same way.
Try to get "help for event".
In entry 9 it says:
This also interesting. Try get "help for event".
Hi Jesper MP
it's another task
and we are just trying to configure the slave and then we have had this problem
Imag of my configuration​
of course i did asyou told me other thread virtule out put in plc become virtule input in Dcs
regarding to event 9 this what i found "help of event"
This event indicates the end of the start-up synchronization of the DP master. If this event does not occur within the monitoring time you have set for the module ready message, the CPU forces the end of the DP master start-up synchronization. The detailed information shows the number of stations that have indicated that they are ready
Many thanks Jesper for your time
This is what i found
The event is only generated if stations are missing at the end of the startup synchronization of the DP master and a setpoint/actual difference is not permitted.
The number of existing stations is always registered as zero in the event.
I dont know the particular error message, so it is mostly guesssing.
The wording sounds to me that the DP port is setup to be a master, but according to your description, the S7 PLC is a slave to the DCS.
Maybe you can post the archived S7 project (.zip file !).
Dear All, I have a KUKA Palletizer machines having Iconics Genesis SCADA installed on its PC. It remained closed for about 7 to 8 years. We are...
963
Hello guys, I have problems with the Porfibus communication to my regulator Siemens Sipart DR 21and my PLC rockwell 1756-L161. So, for the...
2,103
Hey guys, it's been a little while. I'm having a problem that I can't seem to figure out. I'm using a Helmholz FLEXtra® multiRepeater. 6 way. I...
22
5,439
Hello to all, I have a strange problem with establishing the communication between WinCC HMI station and the rest of Profibus network. We have...
3,871
Experts! Need Help In My application i have Siemens CPU 316 WITH APPROX 28 PROFIBUS NODES (including Simovert Master Drive -14N.o.s & IM153 &...
4,874