Profinet communication and PLC in STOP mode
Goran_
Aug 2016
Serbia
Hi all,
I have made a S7 communication (TiaPortal v13) using PUT / GET functions between two S7-1500 PLCs. PLC1 (master) is doing the communication part (one-way).
The problem is that PUT / GET functions On PLC1 do not return fault if PLC2 is in STOP mode.
Does anybody have a good idea how can PLC1 know if PLC2 is in STOP mode? I do have one idea, but I am not sure if this is the right way to go, so I would like to hear some opinions.
Thanks in advance.
Alternatively you can use BSEND & BRCV blocks which are S7 communication but you have to code it in both ends.
But I think with PUT/GET if the partner is not available (i.e. partner in stop mode) then you get an Error from the PUT/GET blocks but the Error output of the blocks is set only for one cycle. Therefore sometimes if you don't latch the error you don't see it while monitoring.
You can also use the T_Diag block to diagnose a connection. It is quite easy.
Another alternative to PUT/GET, which is very easy to implement and diagnose is the I-device option. There is no need for code, the communication is Profinet (RT) and you can easily diagnose it with DeviceStates block.
Of course the old school way is to use a heartbit or lifebit. You send a 1Hz pulse from PLC2 to PLC1. In PLC1 you have a counter that resets from the pulse received from CPU2. If the pulse is not received the counter does not reset and at say 10 counts you can generate an error.
Hi all,
thank you for your responses, they have been very helpful. I have implemented watchdog flasher, and it works correctly.
@grnick50
I can confirm (using S7-PLCSIM) that PUT / GET do not set faults when parnter PLC goes to STOP mode, only if you turn of simulation completely. Error is not set even for a single cycle.
Hello Guys, I want to establish profinet communication between siemens plc and my system using python programming. Which python lib can i use to...
416
Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
43
2,949
I am wondering if anyone can direct me to how to set up communication between a pcb board with ProFinet chip interface and S71200 PLC. I am not...
20
6,114
Hello, please help me with my problem. My application is positioning with Basic positioner of Sinamics S110 (CU305). I use absolute positioning...
4,083
I'm currently working with a Siemens S7-1500 (CPU 1513-1 PN) PLC and a Schneider ATV61(VW3A3327) drive that's integrated with the Profinet option...
194