Programming Advice
draughn
Oct 2002
We are seeking programming advice on a new cooling water application. Our objective is to maintain a Temp. Setpoint of the water leaving the cooling towers entering the process. There are four new cooling towers, each having eight fans. Water leaving the cooling towers goes to a common line with an Analog temperature transmitter which will be our only input to control the fans. We want to start and stop fans in pairs of two with on/off control to maintain our setpoint. We are trying to accomplish this using a Allen-Bradley SLC 5/05 ethernet processor.
We are seeking a wide variety of programming schemes to accomplish our objective.
One possibility would be to use comparison instructions. This would
involve taking the analog input from the temp. transmitter and
scaling it to your desired engineering units. The input could
then be compared to a pre-determined number by which certain
sets of fans would be turned on. Logic may need to be written
so fans would remain on for a certain amount of time to prevent
rapid on/off control.
PID, with some modification
If you made a PID loop out of this, then the
'percent output' would be 'how many fans I
need to operate.
This then, could be fed into a scheme not
unlike the traditional 'pump loading, pump
unloading' concept for sumps and accumulators.
...or not...
Another thing to consider is whether or not to use 2-speed motors. You could chose how many fans you wanted to run at one time, and if the temp is higher than normal switch to high speed before starting additions fans.
Another thing to consider might be VSD's for the fan motors- I'm not sure what KW size you're talking about (I assume huge) but price for VSD's for "reasonable" size motors is not too scary these days- you can then have pretty well infinite control with precise energy requirement matched to the load.
You said you only have one analog input to measure temp. How do you know which fans to run? Is water coming out of each tower all the time? Are the fans that are running tied to any flow control?
Also, are the fans started by motor starters? If so, do you monitor "fan running" with aux inputs? That way you could monitor failure and jump to the next fan if one fails.
So, I'm about to start my first ever project that include a servo motor Here some of the component i bought for the project so far: - PLC: Omron...
392
Concept of the system (Sketch of system attached) **I am blessed to be a member of this community, thanks in advance** System is a chain...
3,026
Hello, starting to get myself into the PLC game and i'm in need of a few support cables. Sorry if this is simple stuff. Sadly the laptop the...
1,735
Hi there, I have an application that I am struggling to find the correct terminology for. From SCADA, the operator should have the ability to...
1,585
So I have been working on a project for the past couple months. we bought 2 machines, and basically I was to interface the two. One Is simply a...
19
5,114