Protection needed for PLC trainer
kapooski2012
Aug 2012
Portland, Oregon
88
Hi everyone,
I’m still gathering my components to build my PLC trainer. I’m sure I don’t need a MCR for protection but I’m sure I need some kind of overcurrent device to protect the PLC. I have a couple inline fuse holders and 1.5 amp breaker a can get a bigger one if needed , a bunch of #16 & 18 wire from SO cords that I cannibalized .
So, what do you suggest, my loads would be I got a bunch of 3 watt lights, a few 120vac ice cube relays, a few nema 1 motor starters (120vac coils) a couple of IEC motor starters, course I would not run everything at the same, I know enough not to blow up everything, I think I have too much for a simple trainer but what the hoot!:geek:
Add up all the loads that you are going to run at the same time.
3 watt lights at 120 volts = approximately 3/120 Amps = 0.025 amps.
120 volt control relay = about 100 VA inrush current/120 = 0.83 amps.
For motor starters, look up the catalog number at vendor's site and find coil volt-amps or rated amps to pull in. Also add the operating current for your PLC(see your PLC specifications).
Or you can use the 1.5 amp circuit breaker.
hi there......i have tryied to put password protection but when i go PLC...access rights...setup this appears i want protection more than...
2,070
I have the power supply in the link below. If we want a breaker to isolate and protect the input side how would I size that correctly being 120...
222
I am having a step7 v5.4 program where the blocks are encrypted and locked. And the manufacturer is stopped the support. Is there any ways to...
214
Let's say I have an inverter fed three phase induction motor drive where in the braking phase (when the motor operates in a generator mode) the...
153
Hello Friends I have a installation with v16, v17, v18, v19, v20. When I tried to open a v20 file, the enable source protection was not enabled...
255