Hi
Newbie with servo and pulse output
I use pulse output cj2m and junma pulse .
I have read the manual but do not understand it
they say:
Output frequency 1 pps to 100 kpps (1 pps units), two pulse outputs × 2 Pulse I/O Modules.
Frequency acceleration and deceleration
rates
Set in increments of 1 pps for acceleration/deceleration rates from 1 to 65,535
pps (every 4 ms).
The acceleration and deceleration rates can be set independently only with
the PLS2 instruction.
Internal pulse control cycle 1 ms or 4 ms (Set in the PLC Setup.)
I have read that the junma driver 1000 pulses per revolutie.
How can i calculate the acceleration and decelleration in pulses?
And the travel distance?
Can some one help me? I want to learn it
Regards
Welcome to the forum.
I deduced from your post that you are using a CJ2M CPU with a CJ2M-MD21 Pulse I/O Module.
"Output frequency 1 pps to 100 kpps (1 pps units), two pulse outputs × 2 Pulse I/O Modules."
This means the module can control 2 axes.
"Frequency acceleration and deceleration
rates set in increments of 1 pps for acceleration/deceleration rates from 1 to 65,535
pps (every 4 ms)."
Minimum pps is 1 and maximum is 65,535. Response time to a pulse rate change is 4 ms.
"Internal pulse control cycle 1 ms or 4 ms (Set in the PLC Setup.)"
Don't mess with this. Ignore it.
"How can i calculate the acceleration and deceleration in pulses?
See attached pdf.
"And the travel distance?"
Travel is based entirely on the mechanical components connected to the servo motor and how much they move for each rotation of the motor..
Thank you for the reply and pdf file.
I use junma pulse
I try to calculate.
move 10mm
1 revolution= 6 mm
10/6 = 1.6667 revolutions
2048*4 pulses = 1 revolution
1.6667*2048*4 = 13653 pulses
so i think i need 13653 pulses to move 10mm
and i try to calculate with pdf file
Regards
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
109
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
144
I am monitoring two BMXDDO3202K digital outputs for their behaviour, they are each for opening and closing, and so the on time affects how far the...
286
Hello, I am using pulse train output to a stepper driver to control a stepper motor. It seems to work fine except when I use a Control Stop...
3,326
Hi all, To make a long and annoying story short, a client has two flowmeters in their water plant and the flowmeter that controls the CL2 dosage...
2,341