Pv600 2711-k6c1

Join Date
Jun 2008
Location
Valencia
Posts
1
I want to comunicate a PV600 2711-K6C1(RIO PV) with an SLC504 but for the printer port. Is it possible?.

When i configure the comunication setting i only be able to choose RIO comunication with 1747-SN.

Thanks for your time.
Frank
 
The printer/upload-download port on your PV can only be used to print or upload/download your PV program. You will have to have the 1747-SN to comm. with your SLC5/04. I would recommend replacing your PV with one that supports DH+ or DF1 protocol.
 