PV900/1000 memory card

Hi Ken,

I manage uploaded the .PVA files from 2 units of PV550.(for backup purpose).
File#1 is currenty linked with SLC5/04 while File#2 is linked with Automax PLC.
We have one new unit of PV550(2711-K5A8, ver 4.48), but once I download File#2, there is error message relating the terminal.

I tried download File#1 to the PV550 without any problem.

I notice the different as follows :-

Application Settings
File#1
Ports
Physical:DH+ Protocol:DH+
Physical:RS232 Protocol:DF1
Keypad

File#2
Ports
Physical:RIO Protocol:RIO
Physical:RS232 Protocol:DF1
Keypad

Communication Setup

File#1
Node Address : 4
Baud Rate : 57600
Node Name : SLC
Node Address: 1
Node Type : SLC-5/04

File#2(RIO)
PLC Type : PLC5/80
Name : Automax
Terminal ,Rack:4
Baud Rate : 230400.

I changed the protocol to DH+ of File#2 but it still not working.

Please comment.o_O
 
What's the error message? Can you post your PV's program ( zip it first)
file #2 before and after the change.
 
A 2711-K5A8 terminal has a DH+ communications port only. It cannot be used on a Remote I/O Network.

Although DH+ and RIO use identical wiring and signal types, the protocol is different and they are not interchangeable.

If the AutoMax interface is a RIO scanner, you need a 2711-K5A1 terminal with Remote I/O.
 
Ken,

Thank you.
For downloading purpose, if I set the terminal setting exactly as File#1, it should be transferred right?.
I will get the K5A1 model anyway.

Mickey,
Attached the file#2 before and after the setting changed.

Thank you
 
Thanks, sinaralf but I believe Ken pinpointed your problem. DH+ is not going to talk to a RIO AutoMax.
 

Similar Topics

Hi All, I have two PV900 I would like to swap, ones screen is dead/dying. from Ser-F Rev C(dying screen) >to> Ser-D Rev S obviously the PVA cant...
Replies
9
Views
2,719
Hello! I am working on setting up a PanelView900 to work with a machine using a SLC5/03. The PV900 only has Ethernet and DH485 ports, so I assume...
Replies
20
Views
7,350
Hey All. I am having an issue with an old PV900 Standard. The part number is 2711-T9C9. The first issue is that on powerup the screen is sittting...
Replies
9
Views
2,608
Iam having a problem tracking down a fault on a machine. The problem is with a separator controlled by a SLC500 (1747 L542B 5/04), this has a...
Replies
1
Views
2,517
The problem started with an error 208 in my PV900 after a program change and download to my slc 5/04. The logic had worked for over 2 years...
Replies
2
Views
2,771
Back
Top Bottom