I have a problem. A client of mine is using a Quantum ACI04000 analog input card. This is a 16 channel unipolar card.
He is complaining saying that all the channels on the card are reading low all of a sudden.. Normally the values should be in the 0-16000 range but now at 20mA the signals are only 15380.
Does anyone have any ideas on what the cause is?
Your help is appreciated.
I Think this is set up using an external power supply? If so, check and see if supply is measuring 24V. Did he just add another input, or are there more inputs that are running toward the 20mA side? If the current draw is greater then what the power supply puts out, the high end tends to start going down.
George
Thanks for the reply.
I will check with him what the PSU is putting out.
The Analog input card sits on a 16 slot backplane. The PSU powers the backplane aswell as all other devices on it such as CPU, comms modules, other I/O cards.
It could be that he is running alot of devices off the same power supply. However, wouldnt that cause the problem to occur from day one itself? He reckons that this problem has just strated happening.
If this is the issue, are the outputs running closer to 20mA then normal? Can he measure the current draw of the Power Supply, and is it close? Did they even add readouts to some of the inputs? One way to test if this is an issue, can he safely remove a few inputs?
George
Hello I was needing help with the proper scaling on a Modicon TSX Quantum- AVI030-00 8 Channel Analog Input PLC card. What would be the proper...
1,498
My first time programming a Modicon Quantum. Not bad so far but I've one question. I have a test rack with a CPU 113 02 and a couple of...
9,398
I am new to the Modicon Quantum line. I have a 140 AVO 020 00 analog output. I have the jumper installed for -10/+10 volt operation. If I put a...
1,599
hi All Can you please help me to find the right software to open Zip backup of 434 12A PLC? Any major steps I need to know when opening? Regards
90
Hello All, Was hoping I could get a little help with Modicon ladder logic. This is the first time I have seen Modicon logic and currently trying...
310