Ok I know this is not the place to really ask this but.
I need to know if 2 0/1 wires are the same as one 300 or 350 cmc wire?
We need wire that I can pull max draw of 280 amps 3 phase.
I am just asking if this wire would work becouse 1 0/1 wire is 150 amps does that mean 2 is 300 amps?
If this is to be inspected you better have the wire size and all the deductions correct or the inspector will not buy it.
If you get it wrong start a fire and then claim your insurance may not allow cause you did not do it right.
Yes you can parallel conductors - very commonly done with larger current and with real large current is the only option.
I would have to look it up in a wire table such as those in NEC.
Dan Bentler
Echo Dan's response but there are a lot of "gotchas" when sizing wire: Is temperature derating required? Are you running all six wires in the same conduit - if so they are derate by 0.8, and so on.
If you are not familiar with wire sizing/ NEC requirements/ etc., find someone who is or you may be creating a future safety problem that can kill someone. 280 A of 460V can make a heck of a fireball when the copper melts, seen it happen and lived to tell about it (no, somebody else screwed up on the motor protection system and I was just a poor PLC coder that energized the motor contactor six feet away from the motor terminals. Ears still ring at times.)
In reference to this thread today I have to install some more C55 contactors with # 4 wire but the wire is standard MTW and will not fit with a...
2,043
I finally have my test/learning bed set up at home. I understand logic and programming, there are some holes in my basic electronics knowledge...
3,414
I have heard that in Europe the most common wire number scheme is a unique number for each wire. As opposed to wire numbers based on "Net" that is...
33
11,435
Hi! I'm going to build a cabinet for US in IEC standard but we change the colors to the customer demand. It's supplied with 3x480VAC and I use a...
29
6,137
I'm probably going to be called stupid for asking this. I have only ever used 2 wire sensors. we would connect one wire to 24 dc+ and the return...
41
7,207