does anyone know if you can make a graphical panel with the quickpanel+ 7inch that you can only open with a password? for example a panel where you can change something that is only accessible to a limited number of people.

i work with pac machine edition 9.8 (pme 9.8)

thanks in advance.
 
The easiest way I've found for an entire panel is to make the visibility if the button that drives you to the panel contingent on the security level of the person logged in. Each login is assigned a numeric value between zero and 999. If you choose to apply security to any action associated with an object on the screen, you assign an appropriate number to that action. The action is only available when the person logged in has a higher number.
 
I can't find anywhere where I can create the account and password list where you can also set the level of security. it would normally right click on the panel under properties. but does not open. where can i create that list? do you know?
 
does anyone know if you can make a graphical panel with the quickpanel+ 7inch that you can only open with a password? for example a panel where you can change something that is only accessible to a limited number of people.

i work with pac machine edition 9.8 (pme 9.8)

thanks in advance.

You should be able to do that with PLC logic. Compare the password entry with the password stored in the PLC memory. If they are equal, then set a bit that opens the protected graphic.
 
The following is cut-n-paste from Proficy version 7 help because that's what I have installed on this computer.

Security for a Proficy View HMI is configured directly in Runtime while the HMI application is running. You must configure security on each individual Runtime machine.

Initially, the User List on a target contains two predefined users:

Master: The master user, with password "control". Users logged in as Master have a Runtime Level of 999, giving them full permissions. This includes the ability to change passwords and edit the User List.

fxDefault: Determines user permissions when no one is logged in.

Before you add new users to the User List, you should:

Log in as Master and change the password. It is recommended that as few people as possible have access to the new Master password.

While you are logged in as Master, edit the View Permissions of user fxDefault as needed.

Note: The Runtime Level of fxDefault is 0, and cannot be changed.

Edit User dialog box
You configure each user in the Edit User List dialog box, activated by the EditUserList script function. This dialog box has the following sections.

Tip: If the Runtime target computer does not have a keyboard, see Using Graphical Elements in View Runtime.

User Name
The log on name of the user. Select the name of the user you want to enter.

Password, Confirm Password
The log on password for the user. Also enter the same password in Confirm Password to confirm password changes.

Access Level
An integer from 1 through 999, which indicates a general security level for the user. The runtime level affects the following:

Whether or not the user can access certain graphical panels, as specified by the View project developer (in the Security property of graphical panels).

Whether or not the user can input values, as specified by the View project developer (in the Security text box when configuring Value Animation).

Tip: You can check the user level in scripts with the #AccessLevel system variable.



Permissions:


Exit Runtime
Select the check box to allow the user to close View Runtime.

Change Data
Select the check box to allow the user to change data from the Animation Inspector or Variable Inspector.

View Inspectors
Select the check box to let the user have access to the following:

Animation Inspector

Variable Inspector

Driver Communication Monitor

Script Debugger

Trend Pen Editor

Panel Selector

Context Menus
Select the check box to allow the user access to View Runtime right-click menus. This applies only to Windows PC targets.

New button
Click to create a brand new user.

Delete button
Click to delete the current user.

OK button
Click to confirm any changes for the current user.

Cancel button
Click to exit the dialog box without accepting changes for the current user.




To add a new user:
In Machine Edition, write a script that includes the EditUserList script function. In Runtime, when the script runs, the Edit User List dialog box will appear.

In the Edit User dialog box, click New. The Add User dialog box appears.

Tip: Clicking the ellipsis button beside any of the text boxes opens an onscreen keypad.

In the User Name box, type the name of the new user.

In the Password box, type a password for the new user.

In the Confirm Password box, type the password again.

In the Runtime Level box, enter a security level from 1 to 999 for the new user.

Note: The user's Runtime Level is checked against the Security level assigned to panels. If the user's level is equal to or higher than that of the panel, the user can access the panel.

Select the Permissions check boxes next to privileges that you want the user to have.

Click OK.



To edit the User List:
In the Editor, write a script that includes the EditUserList script function. In Runtime, when the script runs, the Edit User dialog box will appear.

Tip: Clicking the ellipsis button beside any of the text boxes will open an onscreen keypad.

If you are editing another user's permissions, select the user you want to edit from the User Name drop-down list.

Note: If you have a Runtime Level of 999, all user names are listed in the User Name drop-down list and you can edit permissions. If your Runtime Level is less than 999, your user name alone appears and you can only edit your password.

Type a new password in the Password and Confirm Password boxes.

Edit the user's Runtime Level and Permissions.

Click OK.

Note: A user's Access Level is checked against the Security level assigned to panels. If the Access Level is greater than or equal to that of the panel, the user can access the panel.



To delete a user:
Note: You need a Runtime security level of 999 to delete users from the User List.

In Machine Edition, write a script that includes the EditUserList script function. In Runtime, when the script runs, the Edit User List dialog box will appear.

From the User Name drop-down list, select the user you want to delete.

Click Delete. The user is removed from the User List.
 
It's very simple. All you need is one line. The following is an example of a script attached to the 'Touch' action of a button on a View screen.

EditUserList

Clicking the button runs the script which brings up a list box object with all of the configured users and their security levels. A person logged in at security level 999 can add or delete users and can change the security levels and passwords of any existing users.
 
If you have the GE Sample projects installed, open QPDemo12.
The panel named Tools has buttons for editing users and to logon.
Double-click the buttons to see the animations and scripts.

The sample project PasswordScreen has examples of screens protected by password.
They are more involved than simply setting the Security level of a screen.
 

Similar Topics

Hi, I received the following project from a customer on a QuickPanel Proface 6" that I need to swap to a Siemens Panel. However, I cannot seem to...
Replies
3
Views
344
Dear colleagues, hello to everybody! I have a problem with Quickpanel IC754VBI06SFD-GF Proficy Machine Edition Runtime 6.5 QuickPanel View V2.00...
Replies
7
Views
665
Dear guys, I am not a programmer but I can do simple things myself. I'm stuck with the following. if I want to extract a value from my rx3i...
Replies
46
Views
4,782
Hi all, I need some help in uploading of QuickPanel gp570-sc21 program to PC. I load from QP to PC the project through the working HMI-CAB-C49...
Replies
2
Views
2,028
Having trouble connecting and uploading from a Quickpanel View to Proficy Quickpanel communcates to PLC no problem Quickpanel IP...
Replies
13
Views
2,460
Back