I read that using rack optimization a single CIP connection will be used to transfer IO data from remote card to local card, provided its a digital card.
I was wondering if this applies to generic 1756 module?
Also, say in a hypothetical scenario I have (rack optimized):
Remote EN2T: 200ms RPI
Remote DI (1): 20ms RPI
Remote DI (2): 60ms RPI
Would the communication speed still be dictated by the EN2T card?
I did a few experiments with generic 1756 modules instead of digital input cards, and found that the above example's packet per second is affected by all three RPIs. I did a wireshark capture, and all three affected the comms speed. Disabling rack optimization significantly dropped the pps, so rack optimization is clearly improving comms speed.
Based on my understanding of rack optimization, I anticipated only the EN2T card to affect the pps. Can anyone clarify this observation?
Thanks in advance.
I can't speak to the generic module. Hopefully someone else can.
But Rack Optimization requires two things.
  1. The EtherNet/IP module must be configured for Rack Optimization.
  2. The individual digital I/O modules must also be configured to use Rack Optimation. This setting cannot be changed. If the modules were previously configured with direct connections they must be deleted, re-added and selected to use RO. When this is done, the RPI setting will be greyed out and the value entered for the communications module will be displayed. If you can change the RPI setting for the digital modules then they are not using RO.
It is possible to configure the communications module for RO but still have the I/O modules using direct connections. That is what it sounds like you have configured.
OG
Operaghost that stands true for digital I/O but generic module doesn't have an option to set rack optimization. Yet, I observed that it does have an effect on communication speed.
If that was true, RO setting for communication card shouldn't affect communication then. I guess I'll shoot Rockwell an email.
I have a remote i/o rack that until today was only digital i/o. I am in need of adding some analog io to this rack. The control net card for this...
1,142
I have a Main L73 that will be monitoring 13 remote I/O racks. The remote I/O racks will typically have an ENBT, 2 DI and 1 DO. Of the 13 remote...
2,598
Hello, I have been trying to figure out how to connect to and monitor a DLR that is on a remote rack from my PLC. The local has a 1756-L81E and...
122
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
123
I am very, very new to PLCs. I only have experience with Picos, but I knew enough to save this from the dumpster. Apparently, everything on it is...
617