Read motor current with flex I/O
First...you will need a CT rated for the motor current.
You can get a CT that has 4-20mA out or you will have to buy a signal conditioner to change the standard 0-5Amps from CT to 4-20mA or 0-10V.
Thanks! I will give this a try. I am very sure it is an AC motor as it is a synchronous motor. Do you know how I might be able to measure the torque as well??
It looks like that is a servo motor. Is it a an AC servo? Not a whole lot of information. If it is connected to a servo drive, does the drive have an analog output for current?
Measuring the current in an ordinary 3-phase across-the-line motor is often done with an overload relay that has those features, or with current transformers along with a transducer that outputs 4-20 mA or 0-10 V.
But the Bosch Rexroth motor you linked to is a synchronous servo motor, and is almost certainly being controlled by a servo controller. The current in a servo motor (or even most ordinary VFDs) varies far too fast to be measured accurately by a simple current transformer/transducer/analog device.
Look upstream of the motor for an "Indramat" or "IndraDrive" amplifier or servo controller. That's probably how you're going to be able to get feedback on the power output into another automation system, even if that's through an analog output <> analog input interconnection instead of a digital network.
Yes, the motor is being controlled by a Rexroth IndraDrive controller, specifically the CDB01.1C-SE-ENS-NNN-NNN-S1-S-NN-FW. From my research it appears to have 2 analog outputs (voltage and current). Although, I'm not sure what these outputs tell me. I've looked through the manual but I can't seem to find anything else that can help. I am wanting to also measure the torque of the motor but am unsure how to approach this...
Here's a link to the manual if someone wants to take a look: https://www.cmafh.com/WebsiteCatalo...B01 Project Planning Manual R911295012_08.pdf
Any help would be much appreciated!
I have an AB MPL-320H-H servo motor being driven by an AB Ultra 3000 drive. The motor is directly coupled to a ball screw that moves a linear...
1,837
Some time ago I tried to help Russ solve a motor bearing and motor overheating problem on a system located in Alabama. The drive was Robicon and...
2,222
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
138
Is there a way to use the FAL instruction to do +=2 instead of +=1? I have an array that is organized with alternating "data" and "flag" values...
126
Hi everyone i have a customer, who wants to show an alarm on the machine, if the I/O forces are enabled and set, on at ControlLogix L81E with...
240