Read Tags in Excel From Studio 5000
Factory Talk View Machine Edition. Use ME_DataStore ActiveX object and map to any network location.
Respected Professionals;
Before going to learn Python I want to use xl reporter to fetch data from PLC through rslink and save it to the database. I download the xl Reporter but there is no option for connecting to Rslink.
On which site I download it for a try.
Regards
Thank you so much
Here are a couple dozen lines of python to use pylogix to retrieve data over ~9s at ~1Hz from a PLC (in this case a Micro820), then write those data to a MariaDB/MySQL database. The last two sections, which could be extracted and placed in a separate script e.g. to run once a day, and delete any data older than a week from the database, retrieve those data from the database and write them to an eXcel workbook. The IP addresses of the PLC and the MariaDB/MySQL servers are arbitrary. Explanations of each group of statements can be found via Google. How to setup the MariaDB/MySQL server for such access is left as an exercise for the user; one approach is available at this link. The Micro8xx code is shown in the image below. After that, the beginning of the MariaDB/MySQL database table data; the full table is also attached.
### Cf. https://www.plctalk.net/qanda/showthread.php?t=132004
import sys
import time
import pylogix
import datetime
import pandas as pd
import MySQLdb as Mdb
### Parse command-line arguments: PLC IP address; MariaDB/MySQL DB server IP address; DB username
plcip = (['192.168.1.160']+[a[8:] for a in sys.argv[1:] if a[:8]=='--plcip=']).pop()
ip = (['127.0.0.1']+[a[5:] for a in sys.argv[1:] if a[:5]=='--ip=']).pop()
usr = (['test_log']+[a[7:] for a in sys.argv[1:] if a[:7]=='--user=']).pop()
### Ensure DATABASE 'test_log' and TABLE 'log' exist on MariaDB/MySQL server
Mdb.connect(host=ip,user=usr).cursor().execute('CREATE DATABASE IF NOT EXISTS test_log')
cu = Mdb.connect(host=ip,user=usr,db='test_log',autocommit=True).cursor()
cu.execute('CREATE TABLE IF NOT EXISTS log (tim datetime NOT NULL,tag varchar(32) NOT NULL,val double NOT NULL,PRIMARY KEY tn (tim,tag))')
### Sample data from PLC at ~1Hz, write data to MariaDB/MySQL DATABASE.TABLE 'test_log.log'
with pylogix.PLC(plcip) as plc:
plc.Micro800 = not ('--no-micro8xx' in sys.argv[1:])
for i in range(10):
time.sleep(1.001)
dt = datetime.datetime.utcnow()
cu.executemany('INSERT INTO log VALUES (%s,%s,%s)',[(dt,tag,plc.Read(tag).Value,) for tag in 'et_ms c.Year c.Month c.Day c.Hours c.Minutes c.Seconds'.split()])
### Retrieve data from 'test_log.log' into list of dicts
cu.execute('select * from log')
ads = [dict(ts=None)]
for ts,tag,val in cu:
if ts.isoformat() != ads[-1]['ts']: ads.append(dict(ts=ts.isoformat()))
ads[-1][tag] = val
cu.close()
### Write list of dicts to eXcel workbook
pd.DataFrame.from_records(ads[1:],index='ts').to_excel('test_log.xlsx')
$ mysql test_log -e "select * from log"
| tim | tag | val |
| 2022-02-09 20:37:28 | c.Day | 9 |
| 2022-02-09 20:37:28 | c.Hours | 15 |
| 2022-02-09 20:37:28 | c.Minutes | 38 |
| 2022-02-09 20:37:28 | c.Month | 2 |
| 2022-02-09 20:37:28 | c.Seconds | 25 |
| 2022-02-09 20:37:28 | c.Year | 2022 |
| 2022-02-09 20:37:28 | et_ms | 46 |
| 2022-02-09 20:37:29 | c.Day | 9 |
| 2022-02-09 20:37:29 | c.Hours | 15 |
Thank you so much. You guys are great
I applied a little Python-fu, found a better way to convert the dict-style table to a Pandas DataFrame, and got it down to a dozen and a half statements, wheee!
[Update: the script in the attached .zip should not have the random spaces that are in the post]
import time
import pylogix
import pandas as pd
plcip = (['192.168.1.160']+[a[8:] for a in pd.io.stata.datetime.sys.argv[1:] if a[:8]=='--plcip=']).pop()
ip = (['127.0.0.1']+[a[5:] for a in pd.io.stata.datetime.sys.argv[1:] if a[:5]=='--ip=']).pop()
usr = (['test_log']+[a[7:] for a in pd.io.stata.datetime.sys.argv[1:] if a[:7]=='--user=']).pop()
with Mdb.connect(host=ip,user=usr,db='test_log',autocommit=True).cursor() as cu:
plc.Micro800 = not ('--no-micro8xx' in pd.io.stata.datetime.sys.argv[1:])
for i in range(10):
dt = (time.sleep(1.001),pd.io.stata.datetime.datetime.utcnow(),)[-1]
cu.executemany('INSERT INTO log VALUES (%s,%s,%s)',[tup for tup in [(dt,tag,plc.Read(tag).Value,) for tag in 'et_ms c.Year c.Month c.Day c.Hours c.Minutes c.Seconds'.split()] if not (None is tup[-1])])
### Retrieve data from 'test_log.log', insert into Pandas DataFrame, write to eXcel workbook
n,df = cu.execute('select * from log'),pd.DataFrame(index=pd.Series(name='timestamp',dtype=float))
for ts,tag,val in cu: df.loc[ts,tag] = val
df.to_excel('test_log.xlsx')
Have you tried filling in the data manually?
Run RS Linx on PC and assign a topic name to the processor and retrieve the data that way?
In the Excel cell you would type =RSLINX|TOPICNAME!'TAG,L1,C1'
So if I wanted to retrieve the contents of a tag named Cycle Count from a processor I assigned topic name Machine1 to it would type this in a cell =RSLINX|Machine1!'CycleCount.ACC,L1,C1'
Of course, macros and some other things have to be enabled for this to work in Excel, but it's the way I do it.
Hello friends; I found a code for VBA use in excel to read the Tags values from RSlogix 5000 through RSlink. The code is here: Dim OPCServer1 As...
3,836
Hi everyone. Quick questions. On UnityPro, I want to open and quickly read tags from a .STA files witouth opening the program. I have 30 plc...
146
How to read/write tags using class3 connection with omron Nx/Nj Plc? when i am seeing wireshark packets for my existing connection its shows as...
704
Hello, Just wondering if it is possible to make internal CitectSCADA project tags available to an OPC server. (Schneider OFS). There are...
916
Hello Everyone, I've been trying to write a python code to read input and output tags from a PLC using CIP. I found the service...
25
6,198