Iam trying to have numerical keypad entry into the plc from panelview. The program I have for the panel view screens is all controlled my PLC along the process. My question is iam getting read/write error for the tags in the numerical entry button.
Any thoughts ?
The tags i used for numerical entry button are designated as user defined tags so that they can be shared by few other machines. Iam testing on one but gives me error...
gsajja,
Has this Panelview program worked in the past, or is it new? If it is new, I would guess that you are not reading and writing the tags to the PLC. This could be caused by incorrect tag names in Panelview or wrong addresses in PLC, or there is no communication between the Panelview and the PLC.
Are you using the correct Data Type for the numerical tags? The Bit data type cannot be used to enter Numbers.
I have the tags like this in panel view: for Machine 1
f_enter_number panel_1.enter_number --> write tag
f_check_number panel_1.check_number ---> notification tag
f_show_number panel_1.show_number ----> display tag
f_done panel_1.done ---> hand shake
and i made the above f_ ... tags as user defined tags to that i can use the same for machine 2 i.e... panel_2.enter_number
Iam kinda still having the same read/write error ... any thoughts
I havePLC: CPU S7-300-2 PN/DP (6ES7 315-2EH14-0AB0) And I am using TIA Portal v13 including (Step7 Professional SP1 Update 8, WinCC Professional...
3,249
Hi, Our controllogix connected to panelview thru controlnet with CNB @ node 1 & panelview @ node 9. When i download modified program to the...
8,774
Hi guys, Iam trying to introduce numeric entry code to input the data into the plc. But it gives the write fail error to the tag address in...
1,773
Hi, I am writing java code to read the Main sequence program from mitsubishi A series CPU namely A1SCPU. The default capacity of this program is...
9,083
Hi everyone, I am working on a project that needs to expose the SV (Set Value) of a temperature controller to a SCADA system. SCADA <-...
167