I am trying to set up a msg read and write using a controllogix and PLC5.

All the MSG instructions will reside in the CLX. The CLX is on an ethernet network, which also has a ethernet/DH+ gateway (172.18.50.85). The gateway has 2 cards in a 4 slot chassis, slot 0 is ENBT, slot 1 is DHRIO. This gateway is connected to the DH+ network (CH B) which the PLC5 (node 22) is on.

I am having trouble writing out the address string in the MSG block in RSLogix5000. I know i need to go the IP of the gateway, then i get confused. Is it backplane (0), then DHRIO card (1), CH B (2), then the node of the PLC5 (22)? So 172.18.50.85, 0, 1, 2, 22 ?
 
The CIP Path MSG instruction from the ControlLogix actually only goes as far as the DHRIO module itself.

The module then executes the function contained in the MSG on DH+, and returns the reply over the ControlLogix networks and backplanes.

That's why you designate the channel (A or B) and the target node, and whether it's Local or Remote. In your case if the PLC-5 is connected to Channel B with no other bridges or other devices in the way, it's Local.

Remember that CIP Paths are always pairs of numbers: the Port, and the Address.

Port 1 is the backplane, and Port 2 is the network port for any Ethernet or ControlNet module.

Starting from your ControlLogix, you need to navigate the CIP Path, where x is the slot number of the Ethernet card in the chassis with your ControlLogix.

1, x, 2, 172.18.50.85, 1, 1

1,x = Path to the Ethernet module in the chassis with your CPU.
2, 172.18.50.85 = Path to the Ethernet port of the remote Ethernet module in the "Gateway" chassis.
1, 1 = Path to the backplane and to the DHRIO in Slot 1.
 
Last edited:
Thanks for the reply. I will try this when i get back in tomorrow. I was going wrong and trying to access the PLC within the CIP path, but now understand i only go as far as the DHRIO card and then the rest is set up in the next tab.
 

Similar Topics

Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
179
Hello! New to the forum and new to PLCs in general. We have an ABB AC500 PLC (circa 2012?) and we are using CoDeSys (version 2.something). We're...
Replies
0
Views
654
Hello Ken Roach, Thank you for your quick reply , As informed earlier i want to read P&F Sensor data on Micrologic 1400 series B using MSG...
Replies
17
Views
5,823
Anyone experience of working with these modules and interrogating status of an I/O port? The modules can throw up a red LED indicator to say an...
Replies
0
Views
1,095
Hello, I have a Micro850 PLC that has 5 2080-IF4 plug-in modules attached. Each of these modules are programmed to read 4-20 mA output signals...
Replies
4
Views
2,332
Back
Top Bottom