Reading Modbus Analog Signals in Control Logix
r8er_h8er
Nov 2005
Tulsa
For the first time I have a load of analog signals being transferred into my Control Logix system via Modbus. I have sent analog to a DCS via Modbus by a COP instruction with the analog address/tagname copied to the Modbus Transfer file for 2 - 16 bit words. The DCS reassembles the data to read the analog signal.
Is there a tried and true method for receiving analog signals from a DCS? My blind attempt has been the following:
COP:
Source DCS_2_CAL[100}
Destination TIT_12345
Length 2
I'm sure this has been done before but I'm not sure and will not be traveling to debug this system, I'd like to have it right before I ship it.
I presume you're using a Prosoft MVI56 module. Which exact one ?
The Prosoft module's AOIs end up putting data into specifically named input and output array tags, so yes, the COP instruction is the usual method for moving that data into other tags.
Hello guys, I used modscan32 before to read data using TCPIP based on given IP Address, Device ID and etc. The data I used to read in modscan32...
19
4,112
Hello, i have a curios problem in a modbus tcp reading from a client. The HC900's answer for the variable 20 (holding register 6375) is clear in...
17
3,128
Hi, I have been struggling for a week with FATEK FBs-24-MAR-AC PLC. My goal is to read voltage and current from a powermeter Elnet Pico 5. The...
3,794
Hi all, Has any of you got any example of reading data from modbus tcp, using FBD? I am just trying to get my head around, doesnt look like a...
2,543
Hey guys, I'm working on an existing system for a client where a GE RX3i at a tank/pump station is sending data to their office HMI through a...
3,835