Red Lion Datastation Plus > GE 90/70 IC697CMM742

Cnorez

Member
Join Date
Sep 2013
Location
Lyons, Kansas
Posts
5
I'm having problems getting the red lion to talk to a GE 90/70 through the 742 card via TCP/IP Master SRTP driver. We've been able to get it to talk to our GE 90/30 plc's with the same driver. Any ideas?
 
What error(s) are you seeing?
Verify that your version of the CMM has the GE SRTP protocol and not the older GE TCP/IP protocol, they are slightly different.
For support on the 90-70 you need to contact www.cimtec.com.
 