Red Lion HMI Kadet 304k2
Nov 2013
Ohio
How do I address a B3 bit from Allen Bradley to a tag on Crimson 3? They have options listed as B 003:0000 and Allen Bradly has it named B3:0/0
You have to use a flag tag, in the "data" tab under "Data source" in the "Treat As" drop down, select "Bit Array Little-Endian" then you can select the "Bit Number"
Go back to your AB addressing fundamentals.
An AB address format is file:word. The /bit lets you specify a specific bit in file:word.
B files, despite the name, are files of 16 bit integers. Use the same file:word in Crimson, but specify the bit as shown instead of using a slash bit.
I don't know. My version is Gold 624.005. When I select "pick" thats whats in the popup box to choose from. I'm running DH485 Master for comm.
Why does your tag list the address source as Bxxx:xxxx, but mine lists it as Bx[x]?
My screen shot is from a Redlion connected to a MicroLoigx. Yours is from one connected to a CompactLoigx.
Since the OP was using PLC/5 or SLC500 addressing I used a screen shot that would show how to set it up clearly for him. I was originally going to use this screenshot from another post but decided to post a new one that was less confusing for the OP. Hope that clears things up.
I am having issues getting a Red Lion HMI and Micro830 controller to communicate. I am using the cable here to connect the controller to the RS232...
119
Hi I need to send a null command down a comms port. But in the crimson software when i used /x00 it coming back "Cannot use null character is...
423
Hi Everyone, I am hoping a Red Lion Expert can point me in the right direction. I am experimenting with data logging on a CR3000 10" screen...
605
I have a Red Lion G09 scanning 8 Invertek P2 VFDs via modbus RTU - I've setup necessary comms and tags and all works well. I have a 'Settings'...
1,878
Has anyone ever replaced a touch screen on a legacy Red Lion G3 series HMI?
1,458