Redlion G310 to Lenze 9400 CANOpen
mjoubert
Jun 2007
Pietermaritzburg, South Africa
192
Help Required ....
I have configured the CANOpen expansion option card on the G310 to as SDO Master at 500 KBaud. There are 3 Devices. The 1st is configured as drop 1 pinging register 5EA1 (C00350 in the 9400) and a 2000 ms timeout.
I have also set the dip switches for the Can adresses on the 9400's and changed C00372/2 to 0x641 and C00373/2 to 0x5C1 to enable data channel 2.
The Bus indication on the drive is operational and the Tx and Rx counters are incrementing in the drive, but the HMI is not showing any comms. I'm using IsDeviceOnline(x) to monitor the comms. (Where x is the device number as per the HMI comms setup)
Are there any other parameters in the drives which need to be configured?
Thanks.
Hi All, I have a RedLion G310 panel which talks to a number of devices via Modbus. The G310 has both RS485 ports installed because one Modbus...
2,968
First Post here. I am an old hand with PLCs but new to the G3 and new to BacNet. I have a RedLion G310 HMI talking to a AB CompactLogix PLC. It...
2,299
Hi all I just upgraded our G306 to a bigger G310 display. The G310 just will not serve a web page to the Internet. I can see it on the LAN...
2,228
Has anyone found a good way to put electrical drawings on a G310? I tried the .pdf viewer, but it is painfully slow. It takes about 10 seconds...
2,425
PLC Info: Modicon AEG M//N: PC-A984-145 S/N: 20033182 Comp 984 CPU 8K MEM 1XMB MB+ HMI Info: REDLION Model G310 PT#: G310C210...
2,868