redlion hmi G07 to click plc communications

mike4766

Member
Join Date
Sep 2015
Location
corpus christi
Posts
15
Hello ALL,

I am having problems setting up comms between Redlion G07 and Automation Direct Click PLC.


If the drop numbers (and baud etc) are set identically in both the HMI and PLC then both the Tx and Rx on the PLC lights blink. (indicating PLC is ok?).But i have solid redlight and blinking green on RS-485 port (RS-232)on hmi.i tried using both RS-485 and RS- 232


If the drop number assigned to the PLC slave is anything other than '0' (in the HMI com port set up as assigned to the Click) then I get CommError=2 on the HMI.

Please Help Me!
 
CLICK Basic PLCs have two built-in RS-232 communications ports: one programming port and one that can be configured for either MODBUS RTU or ASCII protocols.
How have you configured the port?
Is the Redlion G07 configured the same way?

Regards,
 

Similar Topics

I'm having trouble figuring out what the actual register is to put into the HMI from the plc. Say DF1 , is it 428673? The HMI tells me that it's...
Replies
0
Views
1,276
I have 8 of these systems all running the same code. Just this one seem to gain about 30 seconds in time everyday. So in 48hrs time will be...
Replies
3
Views
662
Hello, can anyone help with what driver to use in Crimson to communicate Ethernet/IP to a Prosoft PLX31-EIP-MBS gateway. The gateway will pull...
Replies
6
Views
829
Hi, I am using a Micrologix 1400 for a project, and we were supposed to use a 4.3in PanelView HMI. By means of delivery times, that won't be...
Replies
1
Views
985
Hi Experts! I am trying to get a Redlion Crimson 3.0 HMI to talk to a Rockwell Emulator. I imagine I'll have to use OPC DA. Has anyone done this...
Replies
0
Views
1,180
Back
Top Bottom