Regarding A-B 1794-it8

grounded731

Member
Join Date
Jun 2005
Location
Washington State
Posts
1
So this is what can happen if you mix an electrician + Fluke 87 + Flex IO system...;)

Because the -it8 thermocouple modules tend to go out of calibration often and then require an outside contractor to fix/calibrate, I tested to see if there were any possibility of stray voltages and/or spikes causing this to be more a problem than necessary....and found that every 2.5 seconds up to 4.32vdc shows at the tc inputs(1ms max record)...again, measured from ground to the tc+ terminal and got max 19.76vdc...etc.

There is an max vac component of 6.48 measured at ground to tc-.

The A-B manual shows these to be wired correctly, matched to appropriate base, separate vdc supply from the discrete and other analog modules.

Am I seeing something common to PLC's that poll for a measurement?... do I have a noise issue?...or do I just have too much time available to test for this stuff?! :)

Brian J. Pryor
 

Similar Topics

Hi everyone, I need a solution based on the cause and effect diagram, especially a macro sheet or VBA script in Excel, which will help me generate...
Replies
0
Views
78
I know this can be done, but I can't get the router config right. My goal is to physically connect(using an ethernet cable) a device(PLC, RTU...
Replies
9
Views
1,031
Hi, I am connecting an Autonics make stepper driver type, MD5-ND14 to a Kinco PLC (K205 series) this has a sourcing output which cannot be...
Replies
2
Views
1,120
Replies
5
Views
1,944
I haven't had to tune a PID loop in a very long time. It's actually a PI loop for a pulse width modulation s.v. What was the name of that tuning...
Replies
16
Views
4,141
Back
Top Bottom