I tried to use remote OPC using RSLinx gateway. It worked but It seems that the RSlinx must be installed at client too. Is that right? or is that possible only installed RSlinx at server side?
what are you serving? the server should really handle all of RSlinx OPC stuff and serve up whatever you need to the client , but your description is very vague.
Hi andijkt75
You should be able to have RSLinx only installed on the server. There are some security settings depending on the OS that you are using that needs to be changed to allow the exchange of the data via OPC to the client machine.
Depending on the solution you require it might be easier to have the OPC client application on the same machine as the RSLinx server with a application updating a local database with the data in the OPC server. On the client machine you can then query directly to the database.
Andre
Here is a similar thread:
http://www.plctalk.net/qanda/showthread.php?t=30671
GURU, I just tried to retrieve tags from remote OPC Server RSLinx, to be displayed in different computer (client). But always failed to connect to remote OPC server when I choose remote OPC server from infilink.
So I tried to install RSLinx at clint site and make new topic from remote opc server (ethernet link). Then the infilink use the new 'local' topic.
still cannot work
Andre,
I tried to reconfigure again, I tried to connect the client (infilink) in client pc without rslinx, but the infilink cannot connect to remote OPC.
But when I installed rslinx, and run RSWHO, the client rslinx can detect remote RSlinx in Linx Ethernet section. And I can make a new local topic using the remoteOPC.
What's wrong with my system? I tried infilink or OPC quick client from KEP, they could not connect or even detect the remote OPC RSlinx.
runx999 said:
Hi andijkt75
Andre
I remember reading a thread that explained how to use a remote PC running RSLinx Classic as a server to allow an Ecxel spreadsheet running on...
8,331
Hi Can anyone help me with Remote OPC. Actually I have tried OPC on local computer having RSLinx OPC server. A VB application is fetching PLC...
3,717
Hello, Can anyone recommend an expandible IO module with OPC UA? I've deployed the Emerson RSTIO-OM module and it works great, but it has a...
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
190
TLDR: I try to establish the OPC communication between Kepware OPC DA Client to ABB 800xA OPC DA Server. In the Kepware OPC quick client of poll...
864