Sorry, You need interface module as well:
- for LapTop CP5511 (PCMCIA)
- for DeskTop CP5611 (PCI)
and flexible MPI-cable as 6ES7901-0BF00-0AA0
They works in Profi- and MPI-busses (in S7-315-2DB).
Pin order is the same than in drowing above for Profi- and MPI-busses.
Ps. I'm not Simatic admirer, but I have to do this Job for my leaving.
Pinout info
Pin no.:
Code
Meaning
Input / output
NC
Pin 1 is not connected
M24 EXT
M24 EXT return line (GND) of the 24V power supply.
The current load from an external user connected between P24 EXT and M24 EXT must not exceed a maximum of 150mA.
Output
LTG_B
Signal line B of the MPI module
Input / output
RTS_AS
RTS_AS, control signal for Receive data flow. The signal is "1" active when the directly connected AS sends.
Input
M5 EXT
M5 EXT return line (GND) of the 5V power supply. The current load from an external consumer connected between P5EXT and M5EXT must not be greater than 90 mA.
Output
P5 EXT
P5 EXT power supply (+5 V) of the 5V power supply. The current load from an external consumer connected between P5EXT and M5EXT must not be greater than 90 mA.
Output
P24 EXT
P24 EXT power supply (+24 V) of the 24V power supply. The current load from an external user connected between P24 EXT and M24 EXT must not exceed a maximum of 150mA.
Output
LTG_A
Signal line A of the MPI module
Input / output
RTS_PG
RTS output signal of the MPI module. The signal is "1" when the PG/PLC sends.
Output
Shield
Connector housing
You can find this (as well as more useful info) on SIMATIC Support pages (www4.ad.siemens.de), Entry ID 3001321
Best regards,
Sven
bjojo said:
Can you use the MPI cable 6ES7901-0BF00-0AA0 for profibus communications??
yes, on siemens, MPI is connected same way as Profibus, so... pins 4-8-5 and 3
some units, like OP170B have even one connecteur for both, you can setup it like MPI or Profibus-DP, it's about software way and the cable length limit - BOTH ARE JUST 485!
those 24v and 5v is necessary for PC adapter and similar units only ...
<img src="http://www.alteruter.net/temp/plcs.net/upload/mpicable.jpg">
Send signals on profibus between two simatic PLC
I´m trying to connect a 315-2DP to a 414-2DP for sending a few signals on profibus.
I have tryed to use SFB14 and FB14 but it didn´t work. I have a MPI-cable between the PLC:s. I can´t download FB14 to the 315-2DP even if it´s for use with S7-300 systems. Is it possible to do this with this functions?
If not: How shall i do?
I don´t understand the arguments: "ID" and "LADDR". Can som someone please explain them for me.
I need the pinout for anyone of this cables from SICK. These are adapters for a programming tool PGT-10-S. I need it in order to modify the...
2,325
So I had an odd request from a customer for the above. I have written the logic and tested it all in one PLC with only using 7 outputs and 7...
448
Hello all, I hope you're all doing well. I am a complete newbie with a program sent by the manufacturer. I want to use it on a different plc, as...
321
I know it is fairly simple to post a screenshot, but many of us have large screens, so perhaps y'all could take the time to trim those screenshots...
524
Good afternoon all I'm a bit puzzled. 19 inch AB HMI. addressed 192.168.1.22. laptop 192.168.1.10. I can see it in Linx. I can download .mer to...
630