Reverse Scaling (408 to zero) in Logix 500
TimD
Aug 2007
New Hampshire
235
Hi, I have a vacuum transmitter, it's range is 30 to 0 inches of mercury. My spec calls for inches of water, no problem, use SCP to scale 0-16733 to 0-408 and done.
Now the tricky part, the transmitter outputs ~20ma at 'rest' ie. no vacuum.
SO I have a PID loop which works backwards, is there a way to reverse my numbers so that my operator can enter a meaningful setopint and read meaningful transmitter output while looped?
I can't set my scaling block in reverse :(
I also can't rewire or add a signal conditioner. This must be done in software (and tonight!)
Thanks all. Best PLC forum ever.
Tim
You should be able to set the SCP block to to this. There is absolutely nothing that keeps you from using SCP to scale 0-16383 to 408-0. The SCP instruction does not require that input min be less than input max or that scaled min be less than scaled max.
This will give you 408 in N7:6 when I:8.0 is 0 and 0 in N7:6 when I:8.0 is 16383.
Alaric,
Thanks, I gave up when I tried reversing the input side. Should have tried the sacaled side like you pointed out. Works like it should, saves a conversion and potential eror.
Much Appreciated.
Tim
Hi all, I'm having trouble solving a problem I've been working on for several months, and thought you might like a stab at it. The machine runs...
22
1,002
I have a SX2 plc and i'm getting 0-10v analog signal,but i need 10bar analog output in 0v can someone explain how its done
560
I'm trying to add on to a safety circuit and trying to make sure this is fail-safe. My safety scanner needs some muting when things aren't running...
853
Hi, I have issue with acs800 starting the motor in reverse for like 5-6 seconds with a max speed of around -220 rpm before it goes to the...
2,029
I am looking at a 1305 drive connected to a PLC5 via RIO. The drive is working and I was able to get a functional HIM working on the drive as...
1,862