RIO between PLC and SLC
zgozvrm
Jun 2006
Northern California
I have a configuration that is made up of a 16-slot PLC chassis with a 5/20E processor. Channel 1B is set up as a RIO scanner. The chassis is configured for 1-slot addressing and has input modules in the first 8 slots and output modules in the last 8 slots. Therefore, the chassis utilizes logical racks 0 and 1. It is connected to a DCM module in slot 4 of a 7-slot SLC chassis with a 5/04 OS401 Series C processor. The DCM is set up as a 3/4 rack at rack 2 with a starting group of 2. This gives me R/G/S addresses ranging from 022 to 027 in the PLC and 6 words (4.0 to 4.5) in both the input and output table for slot 4 of the SLC. (Actually, only 023-027 and 4.1-4.5, due to the need for a status word in the DCM).
I'm having no trouble passing information back and forth between the 2 processors using discrete I/O addressing (as described above).
My question is this: Is it possible to send data between the 2 processors by using block transfer instructions? If so, how?
1747-dcm
The 1747-DCM only supports discrete I/O data transfer. It does not support block transfers.
You could do your own multiplexing by reserving one of the seven data words as a transaction number, but otherwise it's simple discrete data transfer only.
Also be aware the 1747-DCM is a very seldom used module and has been put on the obsolesence path by A-B.
A similar function can be performed using a DeviceNet 1747-SDN in Slave Mode, or a ControlNet 1747-SCNR in Adapter Mode, so there are other products that will transfer more data, faster, on a modern network.
We have DH+ network on 6 PLC5. We have RSView32 as a HMI. Previously we link HMI with DH+ network by 1784-KT card but we have a problem on some...
3,028
Hi,I'm trying to migrate only CPU from PLC-5 to CLX and I/O modules are still PLC-5 series. I think, the migration works is almost done but I...
1,727
I'm trying to use a message instruction to read the value from a PLC5/20 into another. I have searched the forum, but am getting more confused...
2,136
I was wondering if a 1747-SN installed in two racks containing PLCs could be used to exchange data with each other or RIO?
1,856
Hi there, We have panelview plus installation on DH+ network. Recently we moved from PLC 5 to CLX. Due to CIP connection limitations to optimize...
4,093