Rockwell Data Type Conversion
Saul#75
Jul 2013
Leicester
I have found a BOOL array [64] and I would like to convert it to a DINT array [2] and I'm struggling. I've tried MVM, FFL, CPT, COP, MOV to no avail as I keep getting data type mismatch.
It's in a 1756-L72 running RSLogix 5000 v20
Any pointers would be appreciated.
Saul,
To be able to copy/convert a BOOL[64] array in RsLogix to DINT[2], you need to make an UDT that contains the array (I.E. one member that is of type BOOL[64]. From there you would create a tag of said UDT type. You could then copy this tag to a DINT[2] tag and set the length of 2 in the COP/CPS instruction.
I hope this helps.
-Nathan
Saul,
I hope this helps.
-Nathan
Like your solution....
But I like more simple... redefine the Bool[64] into a dint[2] and manipulate bits as dint[x].y
it may save copy or data handling...
I tend to agree with JGax, steer clear of naked BOOL arrays whenever you can, there is really not a lot you can do with them.
If you must have a BOOL array, then making it a member of a UDT (as already suggested) opens up so many possibilities, including the ability to COP, CPS, FLL etc. Whenever I do this, I make the BOOL array member name something like "number", or "index", so if my UDT tag is called MyBitMap, I would address a single BOOL as MyBitMap.number[274] or MyBitMap.index[274]
When I saw the BOOL array my heart sank. I couldn't understand why you would do this instead of a DINT array.
I didn't want to risk changing the BOOL into a DINT array incase it also required changes to SCADA and other external applcations so the UDT has worked really well with the minimum of disruption. :D
Is it possible to gather OPC data through a 1783-NATR? Searching around, it sounds like OPC data might be blocked by any NAT... Is there any work...
248
We have a product we are now building and are planning on using RFID tags to ID trays of product as they move through the process (5 individual...
1,441
I have seen posts about the Rockwell FactoryTalk ME DataStore Plus ActiveX control to save historical data to a CSV, but frankly the caveats seem...
1,851
I'm using the latest Rockwell CCW to program a Micro 850 and Panelview PV800 - 2711R HMI. I'm having difficulties getting the Panelview HMI tags...
1,830
Hi there, Can anyone suggest the solution to communicate between AB Compactlogix L36ERM controller(Which is having remote flex IOs over ethernet)...
3,697