I am needing some assistance on rounding to 10th in control logix.
I am reading a real number for density out of the meter of i.e 45.23324. I would like to round this to 45.2 and move this number to an AO for an LED Display. The TRN function takes me to the nearest whole number and the same with a DINT which rounds to a whole number. Thanks in advance!
MUL REAL 10 Temp_DINT This will give you 452
DIV Temp_DINT 10 REAL_2 This changes the decimal place back to where it was.
EDIT: For more decimal places multiply & divide by larger numbers. X/|100=0.01 X/|1000=0.001
Just be aware that rounding in control logix handles rounding a little differently when it comes to values with a .5 on the end. It rounds them to the nearest even integer.
1.4999 rounds to 1
1.5 rounds to 2
2.5 rounds to 2
2.5001 rounds to 3
3.4999 rounds to 3
3.5 rounds to 4
4.5 rounds to 4
And so on. I say this, because it may catch you out if you use the methods above, e.g. if your number is 3.45. You may be expecting the answer to be 3.5, but...
3.45 * 10 = 34.5
34.5 rounds to nearest even integer, i.e. 34
34 / 10 = 3.4
I've done a little research on this but still haven't found an answer. I'm trying in RSLogix 500 on a SLC 5/04 to calculate an integer I want to...
4,652
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
318
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
459
Hi, Our customer has bought a machine a CNC wood cutting machine. It states that it need a seperate 16mm2 EMV"ground" in addition to our 5G16mm2...
614
I have a Beckhoff PLC with many AI modules. Most devices are loop powered using the same +24 VDC power as the Beckhoff Bus Coupler and all is...
691