RS links showing AB HMI PV plus 7 as unrecognized device.

engr.saad

Member
Join Date
Nov 2021
Location
karachi
Posts
3
Hello Everyone.
I'm doing this for the first time and got stuck so, I'm posting here.

RS links is showing my HMI on the network but as an unrecognized device. It was a new HMI, I Assigned it an IP address from the IP pool it came up in RS links but as an unrecognized device.

-HMI model is 2711p-b10c22d9p
-RS links revision is 3.71 on PC.
-ME revision on terminal is 10.0.9.290

..Ive tried changing IP address and port.

help me out in this regard.
 
RSLinx Classic doesn't need to recognize a PV+, and version 3.71 is a few years out of date.

You need FactoryTalk Linx, which is tightly bundled with FactoryTalk View Studio (for writing your PV+ application) to recognize the terminal in its upload/download utility.
 

Similar Topics

I'm working on an existing system and I would like to read/write to some additional Powerflex parameters in the Studio5000 logic. My...
Replies
4
Views
781
Hi, I'm working on a project (AB PLC, L85 v34) where we'll have 20 motors installed, all controlled by powerflex 750 series drives. We need...
Replies
1
Views
963
Hi guys, Can you share me any educational links & tutorials for B&R PLC structured text programming? The help section in their automation...
Replies
1
Views
844
Hello, I am modifying a program for a 1756-L61 controller using Logix version 20.01. I am trying to add or change datalinks for several of...
Replies
3
Views
1,536
1st off I'm very new to WonderWare, the program am i needing to modify is version 10.1 The issue that i am having is that while the program...
Replies
0
Views
661
Back
Top Bottom