Rslogix 500 Data Tables Explanation
Ones_Zeros
Feb 2014
at work
367
Hello
I was wondering if someone could give me a good explanation on Data Tables?
Im working in a SLC 500 program and haven't really used it much
all im wanting to do is add some input I/O (Pressure tansmitters) so i can read it back into my HMI software
These transmitters are supposed to be connected to Card 11 - Inputs 1 &2
as you can see by the screen shot bits 1 & 2 are already used on card 11
The entire word is being used (I:11.0 - bits 0-15)
So the way i read it is I:11.1 (I11/16) is the first available input on card 11
would this be input #16
is this right, I think the wiring may be on the wrong input in the PLC
Thanks for the help
When a analog card is used in the slot in question the raw data from that card is put in
the registers e.g I:11.1. I:11.1 is a 16 bit word holding the range of raw data from the analog card. The values will depend on how you have configured the card.
Change the "Radix" ( lower right) to decimal and you will then see the raw data value.
See pdf for raw data value
To begin with, I think you forgot to post your screenshot that you referenced, but I think we can probably get you there without.
That input data table (Table I1) is set up to show an entire 16-bit word on each row. By default, this table shows each word in binary format, so you'll see across the top the binary bit positions in descending order (15 to 0). This can be changed by selecting different options in the "Radix" drop down. Note that this does NOT change any of the values in the data table or how they work, only how they are displayed to you.
Binary input cards will only have one word associated with them. Addresses for binary inputs have to be addressed all the way to the bit level - so if you have a binary input card with 16 inputs in slot 10 the formal address for those inputs will look like I:10.0/0 through I:10.0/15. Shorthand will allow you to drop the ".0" in the middle and simply address these as I:10/0 through I:10/15.
Analog input cards require a full word for each input so they will represent slightly differently. When you reference these inputs in your program, you'll be referencing the entire word. For the sake of argument let's say you have an analog input with 4 inputs in your slot 11. Your inputs will be addressed I:11.0 through I:11.3
Edit - Mickey's too fast
Thanks for the explanation..
Question..Is the a time when you bring a device into a PLC Analog input & not use the entire word? Say a flow meter or pressure transmitter?
Also say if its a digital input, you wouldn't have to use the entire word...correct?
you could use just the bit level ( Example - I:2/9 )
Thanks again guys for your help and patience with me
No, analog inputs use the whole word.
Correct. Each bit represents an input to the card. Some cards have 16 point some have 8 etc.
Hi. I'm doing an upgrade of an old 1400e to a new panel view plus 7 standard using ftv studio v 12,which will be communicating to a slc 5/04 via...
2,626
I have a micrologix 1100 that I am trying to read three data points from it on my safety plc using studio 5000. Any tips or guidance is appreciated.
846
I stumbled onto this behavior the other day, then went looking for old forum posts with the assumption that "there is nothing new under the...
780
Hello All, I am working on converting a program written in RSLogix 500 to Connected Components Workbench. The MicroLogix to Micro800 converter...
1,198
I'm working with a customer to copy one of the machines they designed in-house several years ago. The previous PLC programmer had a thing for...
2,081