RSLogix 5000 VER.19 Scaling 0-10V
ARose110
May 2019
Lebanon,PA
I am new to programming, and I was asked if I could take the 0-10V signal from a load cell and scale it so we could see it on or HMI screen(PanelView plus 1000) as pounds, I am not sure how to go about it, could use some pointers
I'm not familiar with the PV, last time I used one was 16 years ago.
However if you only need to display it some HMI's have a scaling option. so you could scale it like raw = 0-2048 scaled = 0-100.0 It depends on the HMI but by putting a scaling factor in this function can be a simple way.
Some years ago I created a function that scales raw data into anything you want, it takes raw values i.e. 0-32767 and converts it to what ever you need
an example is raw low = 512 raw high = 2048 scaled low = 0 scaled high = 1500. Note this was done for a specific application where internally I needed to convert integer to real to do the calc more accurately, and back to integer (the HMI displayed it as 0-150.0 so even though it was an integer. you could modify it to give out the real value rather than integer.
See attached
Hi Thanks for your time everyone. I am integrating the The endress FML621 over ethernet/ip to RSLogix5000. Any other endress instruments has a...
1,463
Im running windows 7 on vm and studio 5000 is version 27. I opened a clients file this morning to add expansion i/o and drives and as i was adding...
1,428
Hi all, Status update for posterity, and also request for help! I have spent the day installing as much RA software as possible on Windows...
16,021
I'm working on a retrofit job, it is using a Control Logix L55, Ver 13, with Devicenet IO and Ultra 3K drives on Devicenet. Now I need to add in...
8,460
Hello more knowledgable people and old friends, I'm trying (and failing) to connect a ROCON DeltaPoint to the PLC with RSLogix 5000. I tried...
3,002