Rx7i Redundant Contrller Single Bus Network Problem
adnan_hayat88
Apr 2013
Karachi
46
I have an Rx7i Redundant Controller having a Single Genius Bus Network i.e Each Primary and Secondary rack have one GBC. This has happened three times now that when I make both the PLC`s live the redundancy seems to be working fine. But after a few days none of the devices can be controlled by the HMI.Both racks RMX cards show locally ACTIVE. If I STOP one PLC(Active) then all things return to normal. Any ideas why it happens?
Hi All, I have a question would like to ask the experts: my system has two Rx7i PLCs and I'm having them communicate with an RTU (D25) via modbus...
2,072
I have an Rx7i that is dropping out randomly. The modules and rack have been replaced. The CRM is on one of the I/O modules (rack 1 slot 6) so...
1,582
I have a RX7i application that I would like to "convert" (or, perhaps <port> is a better word) to ...well, something else. The code is Proficy ME...
2,634
I need to design an Rx7i based system in which 14 PLC`s will be communicating with a redundant HMI server. Each PLC should also be redundant(HSB...
1,495
One of our customers had a Rx7i redundant Controller system for their plant. Due to some power failure the Controllers power was interrupted. Now...
4,440