Rx7i DROPOUT
Jim66Stang
Oct 2017
ST. LOUIS
I have an Rx7i that is dropping out randomly. The modules and rack have been replaced. The CRM is on one of the I/O modules (rack 1 slot 6) so when it drops out, the machine is down and I can't monitor status anymore. Using only 1 module (for the CRM) it drops out 1hr or 2hrs or 15mins after reset. I am hoping to find a method to monitor voltage, current or comm's signal to zero-in on the culprit. Can anyone offer some tips on past experience. I don''t believe in gremlins, even though we are near Halloween. There is an extension rack with 3 modules on it, but I have reduced this to the main full rack. Thanks Jim .
Solved
FYI...We ended up replacing the terminator on the extension rack. The only thing we had not swapped. It was warm when we took it off. Don't know if the coolant or oil got to it, but the new has it up and running. I would have expected a fault to appear for that.but alas, the older I get the less expectations are met.
Thanks to all. Jim 🍻
Hi All, I have a question would like to ask the experts: my system has two Rx7i PLCs and I'm having them communicate with an RTU (D25) via modbus...
2,066
I have a RX7i application that I would like to "convert" (or, perhaps <port> is a better word) to ...well, something else. The code is Proficy ME...
2,631
I need to design an Rx7i based system in which 14 PLC`s will be communicating with a redundant HMI server. Each PLC should also be redundant(HSB...
1,494
I have an Rx7i Redundant Controller having a Single Genius Bus Network i.e Each Primary and Secondary rack have one GBC. This has happened three...
2,234
One of our customers had a Rx7i redundant Controller system for their plant. Due to some power failure the Controllers power was interrupted. Now...
4,440