Jim66Stang
Member
I have an Rx7i that is dropping out randomly. The modules and rack have been replaced. The CRM is on one of the I/O modules (rack 1 slot 6) so when it drops out, the machine is down and I can't monitor status anymore. Using only 1 module (for the CRM) it drops out 1hr or 2hrs or 15mins after reset. I am hoping to find a method to monitor voltage, current or comm's signal to zero-in on the culprit. Can anyone offer some tips on past experience. I don''t believe in gremlins, even though we are near Halloween. There is an extension rack with 3 modules on it, but I have reduced this to the main full rack. Thanks Jim .